Hello, Called out to look at lighting problem in a house, found a section of cable in loft looking melted, see photos. Anyone know what's caused the cable to melt, don't think its over loaded as its only got 7 lights on it, doesn't look burnt to me. Was thinking it may have come into contact with chemicals?

IMG_20190206_141646.jpg

IMG_20190206_141655.jpg

IMG_20190206_141705.jpg
 
I have seen cable cooked in insulation right next to 50W 12V lamps and transformers, but your pic looks too long a run of heat affected area, implying the conductor really was overloaded. Can you confirm the cable insulation now gone hard and brittle? Or has the cable insulation turned soft and soggy?
 
Yes its from a lighting circuit 1mm T&E cable. It had usual loft insulation over it. I didn't think it was over loaded as its not got black burn marks, it is sort of crispy but is still a little flexible. Looks like two cables melted together, when trying to separate them the plastic sort of tears away from the copper, it is stiff but not crumbly as I would normally expect from a cooked cable.
 
Has there ever been a loss of neutral on the supply to the property? Working for Dno if there was a three phase system feeding a street for example, and the neutral was lost then this can happen, in fact it is one of the worst problems, as all properties on the circuit have to be disconected and inspected, although with modern 1000 volt cables this shouldn't happen.
 

Reply to Lighting problem Melted Cable in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

This from a while ago but reading about everyone elses problems tonight made me remember this one. The original job was the lights in a recent...
Replies
1
Views
1K
Strange on this, we are wiring an extension at the moment and I would like to 3 way the (currently 2 way) landing switch to the new bedroom so...
Replies
14
Views
588
I am not an electrician but am looking for some advice as to how to fix my sporadic light flickering problem that has come and gone for the year...
Replies
24
Views
2K
I have a baffling problem with a newly-installed PIR floodlight and I'd like advice from the forum as to whether it's defective (and should be...
Replies
5
Views
517
have a set of lights that i would like to use plug over battery. have a few plugs and old sets with cables could Frankenstein together if doable...
Replies
5
Views
939

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock