Sounds like a job for the DNOIf everything’s been checked in the board, then it must be outside the consumers installation and must be investigated by DNO.
It could be loose connections in the cutout.
I've had a 100 amp main switch cause similar issues
It’s marked as a pme system and all readings come back satisfactory. Also not sure who asked about IR test but I also done that and readings were high in the hundreds so can rule out poor insulation. I’ve contacted DNO they are coming out next week. I’ve supplied customer with LED lamps and they’ve said it seems to have eased the flickering but still briefly shows signs of dimming/flickering. I’ve read a post on here of faulty main switch which sounds plausible same as rcd but it’s occurring in 2 x rcds so I’ll be better off changing the lot. Then after the DNO disregard the fault being on their end I’m going to change all light fittings and switches then I’m going to change consumer unit.Grant1987 - what Sir is the earthing system in the home? Are the overhead lines marked pme or can you see the lower neutral conductor connected to an earth electrode at some/all of the wooden poles? Has the overhead been modernised to (the ugly IMHV) 4 cable ABC viz aerial bundled cable?
Any electric car chargers in the street?
I will happily thump the consumer unit and the customer ? told them to ring fellow sparks but they’ll be in same boat as me as I’ve spoken to them all. Well the ones I like us sparks do sometimes create a divide you all know what I mean ??If it's either of these or the meter, it might be possible to provoke it by thumping the meter board. A bad connection or contact that heats but doesn't flicker isn't always ticklish but one that flickers often is.
I honestly feel like crying on this one ? I’ll get to bottom of it but it’s now turned into my worst fault I originally put it in top 5 it’s now on topI will happily thump the consumer unit and the customer ? told them to ring fellow sparks but they’ll be in same boat as me as I’ve spoken to them all. Well the ones I like us sparks do sometimes create a divide you all know what I mean ??
Grant1987 - what Sir is the earthing system in the home? Are the overhead lines marked pme or can you see the lower neutral conductor connected to an earth electrode at some/all of the wooden poles? Has the overhead been modernised to (the ugly IMHV) 4 cable ABC viz aerial bundled cable?
Any electric car chargers in the street?
Keep your chin up, we all get those faults from hell once in a while but having solved it the pay off is that you will have gained some knowledge and experience to store away for the next one that pops upI honestly feel like crying on this one ? I’ll get to bottom of it but it’s now turned into my worst fault I originally put it in top 5 it’s now on top
No, there’s none that I’m aware of but I’ll be going back this week and double checkAny electric car chargers in the street?
Want to swap? Got to find shared neutrals tomorrow over 50 circuits in the area, quite a few we can't turn off...I honestly feel like crying on this one ? I’ll get to bottom of it but it’s now turned into my worst fault I originally put it in top 5 it’s now on top
Aww sounds like a bad one had a similar one before but not as many circuits as that disconnecting neutrals one by one on neutral bar with continuity/voltage probes on mcb done the trick.Want to swap? Got to find shared neutrals tomorrow over 50 circuits in the area, quite a few we can't turn off...
Can you current clamp L & N to see if you can find pairs of the same loads, or are all likely to be more or less the same and hard to distinguish on current alone?Want to swap? Got to find shared neutrals tomorrow over 50 circuits in the area, quite a few we can't turn off...