Been to a job replacing 4 X boxes which consist of 2 X 16 amp socket outlets on front and individual RCBO protection for each socket inside the water proof box, now the 4 boxes are on one circuit with the last box being 20m away from panel and is fed in 25mm 2 core, the panel which the boxes are fed has no overcurrent protection or switch, fuse, mcb to isolate them and are tapped straight into the incoming terminals that feed the panel, the panel is fed from a 200amp MCCB at the mains position and has a lot of other panels fed from that MCCB, I’m not sure where I stand as I’m just changing the boxes like for like do I need MWC and the panel needing some sort of fuse at the panel as id say it’s a code 2 and you have no ADS there
Thanks
 
The current carrying capacity of the 25mm won't be north of 100A and that's before considering any rating factors or voltage drop. I take it there's a 16A RCBO protecting each 16A BS4343 socket, therefore the weakness is the supply cable and the fact there's no upstream protection or means of isolation, if it's straight off the incomer. Don't touch it with a barge pole, unless your quote to fully correct the installation is accepted.
 
The current carrying capacity of the 25mm won't be north of 100A and that's before considering any rating factors or voltage drop. I take it there's a 16A RCBO protecting each 16A BS4343 socket, therefore the weakness is the supply cable and the fact there's no upstream protection or means of isolation, if it's straight off the incomer. Don't touch it with a barge pole, unless your quote to fully correct the installation is accepted.
Thanks and yes each socket has it’s own individual RCBO and I’ll let customer know the situation
 

Reply to Like for like replacement test or not in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I recently purchased a rural property in Arizona. The property receives power from APS, the local electric utility. Power arrives from the...
Replies
3
Views
831
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
Hi, I’m an industrial electrician, so when it comes to DB regs and such my experience on them is a little limited. I need 2 x 16A 3 phase supply...
Replies
1
Views
678
Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
674
Been round to a house to quote to replace some storage heaters for new panel heaters and came across a strange (to me at least) way of wiring the...
Replies
23
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock