  1. Sparky12021986
    Offline

    Sparky12021986 Guest

    hey everybody just need clarification to a question i think i got the right answer so here goes....

    Q. List in the correct sequence the tests required for an installation to comply with BS 7671.

    A. Continuity test
    A. Insulation resistance test
    A. Polarity test
    A. Earth fault loop impedance
    A. PSCC and PEFC if not determined by enquiry of the distributor.
    A. Functional testing including, testing of RCD's and operation of all switchgear.
     
  2. i=p/u
    Offline

    i=p/u Electrician's Arms

    earth electrode/ze is missing between a and a
     
    • Like Like x 3
  3. supasparxs
    Offline

    supasparxs Electrician's Arms

    Location:
    Leigh, Lancashire
    Visual inspection should also be before any of thoses
     
  4. Sparky12021986
    Offline

    Sparky12021986 Guest

    sorry there should of explained a bit better but i dont need an earth electrode test done as that is only required for TT systems i am working with TN systems so all is needed is a Earth Fault Loop Impedance test..
     
  5. Sparky12021986
    Offline

    Sparky12021986 Guest

    thanks just added it to my list...
     
  6. i=p/u
    Offline

    i=p/u Electrician's Arms

    your pretty dam close..
     
  7. Sparky12021986
    Offline

    Sparky12021986 Guest

    ok so if i am pretty dam close as you put it what else am i missing...
     
  8. malcolmsanford
    Offline

    malcolmsanford Electrician's Arms

    do I have to get my coat ............................phase rotation ..................sorry gather it was single phase
     
  9. Sparky12021986
    Offline

    Sparky12021986 Guest

    yes it is single phase..
     
  10. i=p/u
    Offline

    i=p/u Electrician's Arms

    you just writting earth fault loop impediance, doesnt buy it for me, plus, ring final circuit conductors, and if was new install would differ from exisiting,
     
  11. Sparky12021986
    Offline

    Sparky12021986 Guest

    ring final circuit conductors comes under the same test as continuity, continiuty of conductors are to include protective conductors including main and supplementary bonding conductors, also ring final circuit conductors including protective conductors..
     
  12. JUD
    Offline

    JUD Electrician's Arms

    Location:
    East Yorkshire
    I wouldn't count visual inspection in the sequence of tests. They are completely seperate, hence why they call it Inspection AND Testing.

    Inspection is done using the senses. Testing is done using test equipment.
     
    • Like Like x 4
  13. i=p/u
    Offline

    i=p/u Electrician's Arms

    nah, there seperate tests and if you look at the lists in most books there separate, all depends on what level you doing this... but your pretty dam close ;)
     
  14. Sparky12021986
    Offline

    Sparky12021986 Guest

    On site guide chapter 9 page 75

    9.3.1 Testing checklist...

    Please read..
     
  15. i=p/u
    Offline

    i=p/u Electrician's Arms

    im getting proximity to electrical and other services,,, you wouldnt be using he book too older regs, hahah

    your right to the on site guide, but this opens up completely when your a man, and what about vold drop..

    your pretty dam close tho

    ok your pretty much right
     