Discuss Live working on DC -48V systems in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
17
Afternoon all,

Just after a bit of advice and clarification on an issue that was presented to me today. For a bit of background I work in the telecoms industry and today was notified of a manager for a client I work for, advising live working in DC distribution boards. More specifically, isolating the specific MCB which said circuit relates to, removing the relevant equipment, and then removing the relative MCB from the DC board without isolating the whole thing.

As far as I'm aware and in all of my recent teachings, it's simply that live working is not permitted under normal circumstances (regardless of AC/DC and system voltage) and unless it is absolutely unavoidable - which simply isn't this case. This was advised due to wanting to minimise downtime for radio equipment by only isolating the specific circuit which as I've said, is fine, but the removal of the MCB after this shouldn't happen without the whole board being isolated surely?

Thanks in advance.
 
You are quite correct with regards to working live. Why not leave the breaker in place.
 
Will you have to remove the circuit from the board because it will be live even with the mcb off.
 
Will you have to remove the circuit from the board because it will be live even with the mcb off.

I don't quite follow, why would it be live even with the MCB off? I don't have all the details, I'm not involved in this work myself but I was asked for advice by my manager as he'd seen this information handed out and thought it was wrong.
 
If you are going to isolate the mcb at the board to remove the circuit the rest of the board will still be live.
 
There is a main isolator within the DC board which could be used, but this is exactly what the memo wrongly advised against. Really either the circuit should be isolated by the individual MCB - then the item removed but the cable would remain in place (if their priority is downtime). Or the other option (if their priority is to remove equipment and all redundant cabling) is to isolate the entire DC DB and remove the circuit & MCB.
 
If you are going to be working inside a live DB then you should be following a documented safe system of work which would usually involve temporary insulation/shielding, PPE, a specific order of operations, supervision etc etc.

As a trainee you should definitely be receiving proper live working training and full supervision if you are to do this.
 
If you are going to be working inside a live DB then you should be following a documented safe system of work which would usually involve temporary insulation/shielding, PPE, a specific order of operations, supervision etc etc.

As a trainee you should definitely be receiving proper live working training and full supervision if you are to do this.

Absolutely agree, and I wouldn't do that. It rang alarm bells to begin with and that's why I wanted to gather more information here before confirming my state on this!

Like I said, this work does not directly affect me at this moment but it is work that will probably make its way to me eventually. Thanks for all your advice guys.
 

Reply to Live working on DC -48V systems in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi, I have a dual RCD board made by Hager installed a couple of months ago. It is high integrity, which I understand to mean RCBO’s can be...
Replies
17
Views
3K
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
1K
I had a PV system installed by a local reputable manufacturer last autumn; since then, I've received conflicting advice regarding the consumer...
Replies
2
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock