Hi all, i need the calculation applied to work out the current per phase for a 3 phase circuit.
Found a 9.1 kwatt heater on a 25A triple pole mcb (60898), so on single phase load divide by volts = amps, but this is not the case for 3 phase, any help much appreciated?????
Oh i found the heater on a hospital periodic, the cable used was a 4 core 2.5mm armoured...............
 
Just in fun (not a dig at you P&S) I worked out the PF that would be required to get 23A for 9.1KW @ 400V. It comes out at a staggering 0.375 lagging.

I’ve only ever seen figures like that on huge induction furnaces (they had massive capacitor banks linked to them). The cables had that much current flowing through them they had to have water pumped through to keep them cool.


As I said I did it for fun as I like playing around with maths.
 
Last edited by a moderator:
i was testing this circuit as part of a periodic on the hospital, saw the cable size feeding this heater rated at 9.1 Kwatt and looked a bit on the slim side copper size wise, but couldnt think of the calculation required, thanks for your help as alaways its good to discuss )))))
 

Reply to Load calc for 3 phase supply?????? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I am trying to understand 3 phase volt drop. I understand single phase VD. Lets say we have a 70 meter run of 35mm, 5 core cable from the supply...
Replies
6
Views
2K
So, the actual job is on a farm. I think I'll keep things simple at the moment and just ask about voltage drop. I'll come on to earthing and...
Replies
11
Views
2K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
Hi all, I have been asked to install individual three-phase supplies for a band saw and table saw. Having trouble figuring out the correct cable...
Replies
15
Views
2K
About 15 years ago, after having had a modern consumer unit fitted, and prompted by our electrician, I asked my then energy supplier (Tonik) if...
Replies
25
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock