Discuss Looking for opinion on whether this scenario is compliant in the UK Electrical Forum area at ElectriciansForums.net

T

The Ghost

Went to daughters house to replace a couple of broken sockets and did a Zs and RCD test after replacing. CU was replaced and notice on it said inspected 2015. Plastic dual RCD 30 ma/Main switch 60947-3 isolator. System is TT. (100ma RCD?)
Zs at socket was 11.75 ohms L-PE 2.64 ohms L-N. No bonding present to services. Suggested my daughter might get the council in to check it out. Had a phone call today and electrician said it is all compliant! He also said it disconnects in 0.37ms and I asked to talk to him he would not. He said I was just trying to make money, if only he knew? Apparently he fixed the bonding in a few minutes.
I said to my daughter tell him it should be 0.2 (the property is not cross bonded as in the exception to table 41.1) he said that was the case 20 years ago and I needed to get up to date. Okay!
I must confess to be a little bit taken aback by this and thought I would do a sanity check with the forum members. I do have Amd 3 BS7671 by the way i.e. 2382-15 so I think I am up to date.
Essentially I am of course concerned for my daughter, and what appears to be possibly a cavalier attitude. I told my daughter to get a copy of the report and tests so we await that. Am I being concerned over nothing or just plain stupid??? Tin hat on.
 
The 0.37mS time for the RCD would comply at both 1x and 5xIn so would pass.

As for plastic board in 2015 all depends on when the installation was designed, might be the council has a generic design for those properties.
 

Reply to Looking for opinion on whether this scenario is compliant in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
783
Hi everyone Recently I have come across an advert of someone selling Afdds C type and the person mentioned the need to sell because Zs was too...
Replies
16
Views
3K
I'm having a bit of a disaster at the minute and would like an honest opinion. I am having a gas stove fitted in the corner of my room and...
Replies
6
Views
1K
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
876
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock