Discuss Loop method using Fluke 1653 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

H

hahol89

Hi all!
I tried to measure earth resistance by loop method using fluke 1653 at MR system (TN) in hospital. But got abnormal results. The primary (upper) display showed 0.16 - 0.2 (loop impedance) and secondary - 0.0 - 0.1 (earth resistance)
Is there some limitations using this method? Cant find information about it.
Thank you!
 
What is Ra?
Let me explain, i am responsible for power & grounding audits in my company and i got measurement procedure from my previous colleague. But i see that this is wrong way to measure earth resistance with loop method. I want to know whats is wrong? I saw information that this measurement acceptable for TT systems but not for TN. Is it true?
Thank you!
 
Ra is the resistance of an earth electrode to earth, it is the value given on the second line of the display after the test you have done. This is not the best way to measure Ra, it is better to carry out a proper earth electrode test wherever possible.

However all of this is irrelevant to your TN supply, what exactly are you trying to measure. And are you a qualified electrician?
 
Ra is the resistance of an earth electrode to earth, it is the value given on the second line of the display after the test you have done. This is not the best way to measure Ra, it is better to carry out a proper earth electrode test wherever possible.

However all of this is irrelevant to your TN supply, what exactly are you trying to measure. And are you a qualified electrician?
No. i am not electrician, i am an installation engineer (medical equipment). I need to measure earth resistance that our equipment used. i can carry out measurement only in our disconnet panel located neer equipment, so its impossible to use 3-pole measurement or similar methods. i think it was purpose to use fluke 1653, but i should to understand its not best way or it is wrong way?
I think the best decision it is clamp on method, for example fluke 1630. What do you think?
 
This is the quick reference guide for measuring the earth fault loop impedance of a circuit for the fluke 1653b.
1653b quick reference Z1.jpg
If you have RCD protection then you would need the no trip setting, if not then the high current test is better.
if you press F3 then you will move off the RE measurement and back to the fault current.

If you need more information then this is a link to the user manual.
 
Richard, thank you! But i already saw this manuals. My question is limitations for this measurement. Is it acceptable for TN systems? Should i disconnect earth conductor from earthing busbar?
I found next topic and i want to understand is loop method the same with method in part 4 of this topic.
Thank you
 
Using the Z1 method, from the Fluke 1653, of measuring the earth fault loop impedance is the de facto standard for TN systems.
The limitations are that the measurement is not very accurate at very low values of EFLI due to the limited resolution of this type of meter.
Using the no trip measurement limits the test current to about 15mA and so introduces noise on the measurement that reduces accuracy.
contact resistance on the connections can also affect the result so good connections are essential.

This method can also be used on basic TT systems for a reasonable approximation of the true value of the resistance of a an earth electrode.
It is not suitable for accurate measurement of earth electrode resistance for which a earth resistance tester would be required.

In order to gain a value for Ze (the external loop impedance) of an installation it is necessary to only measure at the origin once all bonding conductors are disconnected (or disconnecting the main earthing conductor and measuring to that) otherwise a falsely low value of EFLI might be obtained due to parallel resistance paths via the bonding.
This requirement does not obtain where you are measuring the Zs of a final circuit.
 
In order to gain a value for Ze (the external loop impedance) of an installation it is necessary to only measure at the origin once all bonding conductors are disconnected (or disconnecting the main earthing conductor and measuring to that) otherwise a falsely low value of EFLI might be obtained due to parallel resistance paths via the bonding.
This requirement does not obtain where you are measuring the Zs of a final circuit.
Im sorry for stupid questions but what is final circuit?
 
A final circuit is a circuit that directly powers an item of equipment.
i.e it is not a circuit to or between distribution boards.
e.g the circuit powering a your lighting, boiler or socket outlets.
 
Thanks all! But I will repeat my questions
But got abnormal results. The primary (upper) display showed 0.16 - 0.2 (loop impedance) and secondary - 0.0 - 0.1 (earth resistance)
I followed all steps from manual. What I made wrong?
 
Thanks all! But what I made wrong that I got results (The primary (upper) display showed 0.16 - 0.2 (loop impedance) and secondary - 0.0 - 0.1 (earth resistance))? I followed all steps from manual.
 
It is no good saying you have abnormal results and not telling us what you think is abnormal about the results.
A 0.16Ω or a 0.20Ω resistance is a reasonable figure for an Earth fault loop impedance.
The Re result is immaterial as it would only apply if you wanted to know the resistance of the earth component of the loop, however it is an acceptable value, slightly lower than I would expect, but acceptable as a value.

If you wanted to know the prospective earth fault current (PEFC) then you need to press F3 on the tester to change the display.

Therefore unless you can say what you think is wrong we cannot progress further.
 
Sorry!
Customer measured earth resistanse with 3-pole method (1.6 ohms measured value) and asked us to check this results, so i tried it and got 0.16 - 0.2.
 
earthing conductor resistance

To obtain an accurate resistance measurement of an individual conductor, such as r2, you will need to perform a continuity test. This is a dead test. You will need to disconnect one end of the conductor and measure the resistance using your Fluke set to continuity from one end of the conductor to the other. This method of measuring r2 is called the 'long lead method'. See IET Guidance Note 3 for more information on dead testing.

Everybody, who knows anything on here has given you the right advice regarding the no trip earth fault loop impedance testing with your fluke. Perhaps, you mean earth leakage...

Or perhaps this is a wind up?
 
To obtain an accurate resistance measurement of an individual conductor, such as r2, you will need to perform a continuity test. This is a dead test. You will need to disconnect one end of the conductor and measure the resistance using your Fluke set to continuity from one end of the conductor to the other. This method of measuring r2 is called the 'long lead method'. See IET Guidance Note 3 for more information on dead testing.

Everybody, who knows anything on here has given you the right advice regarding the no trip earth fault loop impedance testing with your fluke. Perhaps, you mean earth leakage...

Or perhaps this is a wind up?

You absolutely right, i mean earth leakage resistance, sorry but this is difficulties of translations))
 

Reply to Loop method using Fluke 1653 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Afternoon all, How do i solve these two questions, Feel like am missing something simple. doing my head in lol. I need to learn the calculation...
Replies
24
Views
4K
H
Earth Electrode Resistance Testing 2395 Hey guys, I'm up for my 2395 soon, although I understand how each of the three methods is carried out I...
Replies
4
Views
2K
S
Hi Guys, I've just swapped over to a Fluke 1654B MFT and I have a question about measuring the Re using the loop test function. Anyway, on the...
Replies
4
Views
3K
Another long one from me ... I hope that it covers all the bases and is a more thorough approach to the subject. It is my first design work so...
Replies
44
Views
6K
J
Guys (n' girls of course) I have just started using a 1653B FLUKE and when testing earth loop impedance Ze (ie. impedance of supply - tested at...
Replies
10
Views
26K
1shortcircuit
1

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock