Arms
Reaction score
109
Hi all, while testing Zs on a ring final circuit i found one socket to have a particularly low Zs. All others were reading between 0.25- 0.30 but this one was reading 0.08-0.09. Its got a brand new Crabtree double socket installed. A full RFC test has been carried out, and this is the only socket with a reading this low. Obviously i know its better than high, but was just wondering if anyone could shed some light.
Its a TNS system, Ze 0.26
 
operator error. with a Ze of 0.26, it's impossible the get a Zs that low.
 
Last edited by a moderator:
check the leads, batteries and the fuse in back of your mft is nice and tight. then zero/null your leads. retest some of the others to check consistency then re test the problematic one. should give you an indication of whether its the mft or not.
I often find that if i dont use the kewtech kt64dl mft for a few days - say over a bank holiday weekend then on the tuesday the results can be fluctuating a bit, so i now do the things i said above each morning. and my results are now much more stable. i dont seem to get weird anomalies like before.
 
check the leads, batteries and the fuse in back of your mft is nice and tight. then zero/null your leads. retest some of the others to check consistency then re test the problematic one. should give you an indication of whether its the mft or not.
I often find that if i dont use the kewtech kt64dl mft for a few days - say over a bank holiday weekend then on the tuesday the results can be fluctuating a bit, so i now do the things i said above each morning. and my results are now much more stable. i dont seem to get weird anomalies like before.
Its the first time ive used it since its been calibrated, just changed the batteries this morning. Ill try everything again tomorrow!
 
check the leads, batteries and the fuse in back of your mft is nice and tight. then zero/null your leads. retest some of the others to check consistency then re test the problematic one. should give you an indication of whether its the mft or not.
I often find that if i dont use the kewtech kt64dl mft for a few days - say over a bank holiday weekend then on the tuesday the results can be fluctuating a bit, so i now do the things i said above each morning. and my results are now much more stable. i dont seem to get weird anomalies like before.
Its the first time ive used it since its been calibrated, just changed the batteries this morning. Ill try everything again tomorrow!
 
I often find that if i dont use the kewtech kt64dl mft for a few days - say over a bank holiday weekend then on the tuesday the results can be fluctuating a bit, so i now do the things i said above each morning. and my results are now much more stable. i dont seem to get weird anomalies like before.
I had one of those at my last place; it's a really easy tester to use but I found almost bang on the day it was due for calibration I started getting really high readings when I measured Zs using the probes. For some reason it was fine using the plug adaptor, it was just off using the probes. It was fine again after calibration.
 
operator error. with a Ze of 0.26, it's impossible the get a Ze that low.

Hi - can't have Zs lower than Ze, so likely a measurement error and I'd just redo it :) .

I've always thought that, but what about the following scenarios..

1. Property is TNCS or TNS. The metal pipework on the bonding is deep underground and aids in the Zs (but is not included in the Ze as the main earth has been removed from the MET). If the additional earth pathway created by the bonding outweighs the R1+R2 couldn't the Zs<Ze?

2. Also, what if you have an Ra = 200Ω (TT) and the bonding of the property is also attached to the bonding of the adjacent property which is TNCS? Wouldn't the Zs of the property be influenced by the adjacent properties TNCS?

3. Ra = 200Ω (TT). Pipework on gas/water deep underground. Would this not influence the Zs and perhaps make it <200Ω

Just having a sit in the garden and pondering these deep matters :)
 

Reply to Low Zs at socket, Any ideas?? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
I've just picked one of these up on a famous auction site. The voltages, low and high resistance ranges all appear to be working fine but it's not...
Replies
7
Views
255
A silly fault in a circuit only 4m long is currently eluding me! This is ECIR remedials of a landlords supply in a block of flats. Circuit 2 =...
Replies
3
Views
844
Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC...
Replies
18
Views
2K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
780

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock