So as Geoffsd and Serpico said:
for a 100A domestic supply, the Ia value would be either 1200 at 0.4s or 630 at 5s
To which the higher would make the maximum permittable resistance of the main bonding conductor is 0.041 ohms if R< 50/1200
The cable measured was directly from the conductor at the MET to the bonding clamp using croc clips?
So would a resistance of 0.25 Ohms mean that the bonding conductor is unsafe as the resistance is too high in the event of a fault?
Forget about resistance, select the right size job done. If the bonding conductor is in place and the right size, just test its resistance so that it relates to length and csa.