Can you see professor Boff, how a simple piece of writing can be miss understood, so therefore someone with your capacity to soak up information at such an incredible rate should in all probability probably be a lot more humble.
 
The 0.05 value is the value below which potential difference should be, between simultaneously accessible extraneous conductive parts. Example of which is a gas pipe and a water pipe next to each other. Test between the two.

Even if both are 10mm bonded individually back to MET, if the difference between the two is greater than 0.05 then they need to be bonded to each other.
If that is the case then that would be supplementary bonding which, unless in a bathroom or similar location, is not required.

The 0.05 figure is not a value to be achieved between MET and bonding point taking into account the value of resistance of the cable.
But that is, indeed, what is required in my old copy of GN3 (has it changed?).

So - if still required, it must be agreed that it is not possible to achieve this with a conductor whose own resistance is greater than 0.05Ω.


It also states that supplementary bonding conductors must have a resistance of 0.05Ω or less.
 
The 0.05 ohms has nothing to do with the value of the bonding conductor at all, it or any other measurement you will be able to work out the length of any size cable, so once again nothing to do with the bonding conductor max value.
 
If that is the case then that would be supplementary bonding which, unless in a bathroom or similar location, is not required.


But that is, indeed, what is required in my old copy of GN3 (has it changed?).

So - if still required, it must be agreed that it is not possible to achieve this with a conductor whose own resistance is greater than 0.05Ω.


It also states that supplementary bonding conductors must have a resistance of 0.05Ω or less.

i wouldnt consider anything written in the guidance notes as regulations that need to complied with to be honest Geoff.
 
First time i've read this thread but the most amusing point of it for me is the fact post #14 explained the 0.05 value and it seems to have taken a day for many others to catch up....
 
I am perfectly willing to accept thanks for the information given in Voltz's posts if you think it is valuable, after all I missed much of the Wales Vs France game to explain it to him in detail! ;)

sorry bud, I did not take credit for your valuable input, but perhaps i should have given you more direct credit for your enlightenment. I remembered something along the lines of which you were trying to explain to me a while go and this brang it all home to me while i was perusing the forum and keeping half an eye on a stalemate game at the time.

Thanks for the chat and at least the boys done good after we finished talking!

xx
 
The 0.05 relates to the bonding connection, not the conductor length. This is to conform the clamp is connected to the conductive part with a low resistance joint. (i.e. paint removed from pipe). This relates over to the 0.1 + R of lead used in the COP for portable appliance testing, as there are 2 points of connection (0.05+0.05=0.1)
The purpose of the main protective bonding conductor is to equalise the potential, so we only see the volt drop (touch voltage) of the R2 conductor, between conductive parts under fault conditions. If no bonding is present, we will see the volt drop of the R2 conductor, plus the volt drop of the external earth. Obviously this will be greater in TT installations, due to the higher resistance in the earth electrodes.
 
The 0.05 relates to the bonding connection, not the conductor length. This is to conform the clamp is connected to the conductive part with a low resistance joint. (i.e. paint removed from pipe). This relates over to the 0.1 + R of lead used in the COP for portable appliance testing, as there are 2 points of connection (0.05+0.05=0.1)
The purpose of the main protective bonding conductor is to equalise the potential, so we only see the volt drop (touch voltage) of the R2 conductor, between conductive parts under fault conditions. If no bonding is present, we will see the volt drop of the R2 conductor, plus the volt drop of the external earth. Obviously this will be greater in TT installations, due to the higher resistance in the earth electrodes.

Quite, think about the clamp and the pipe, simultaneously accessible conductive parts...
 
Seems to me a few varied explanations yet not one definitive answer, 0.05 appears to be a standard value used with no understanding of the reason.

Be nice to know the correct theory
 
this value of 0.05 ohms is irrelevent regardless of how its measured , you size the bonds as per the requirements of section 544 bs7671.
no mention of maximum resistance or length is even mentioned in the regs.
when push comes to shove , the numbers suggested in the guidance notes dont mean jack , theyre just suggestions for the many different ways of compliance.
 
"Does main bonding in every circumstance always need to be under 0.05. main bonding in a house where the main water was moved has 10mm cable but resistance of 0.25 ohms"


a few of us have already stated, the fact that it's over 0.05 on a relatively short run is indicating that it's not continuous and needs investigating.

- - - Updated - - -

Noooooooooooooooooooooooooooooooooooo it does not have to be so
 
Last edited by a moderator:

Reply to Main bondage in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi I have a 1st fix domestic install on the go and need to leave a socket for other trades to use after me. There is no main bonding at the...
Replies
7
Views
822
I have a main panel beside my meter on the house built in 1987. Then a 4 wire feed into a 200 amp panel on an inside wall of my basement. All of...
Replies
1
Views
379
Not sure on this one. Mains water is coming up from the ground in lead pipe in bathroom. 2 inches of copper pipe before the stop tap. All...
Replies
4
Views
1K
Hello, my incoming supply has one main fuse that feeds the next door naghbour it leaves my house to go next door as shown in picture..it's the...
Replies
4
Views
796

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock