Today i have been asked to give an independant opionion on electrical work undertaken by another electrician on a commercial property.

There has been work done to "improve the mains bonding arrangments".

The buildings supply is a 100a 3 Phase TN-C-S. Connection to this is by a 50mm2 single, crimped and bolted to the side of the cut-out connecting to a small domestic 8 way MET. There is then a 16mm2 cpc supplying the D.B which is fed from a 100x100 trunking between the supply and the D.B.

Before the work was carried out there was 2 x 10mm2 singles connecting the MET to the incomming gas service. He has now cut these back, crimped and screwed them to the side of the 100 x 100 trunking. Surely this has only made the situation worse ??

543.2.2 does say that a metalic cable management system can be used as a protective conductor but surely not for mains bonding as this must be connected directly to the MET?

This is by no means the only issue here, however i dont want to list "Protective bonding conductors not connected directly to the MET" if this is not actually incorrect.

Thanks
 
youre right.
main bonds should be continuous and unbroken en route to the services.
only cpc's can use metal containment as a carrier.
i'd give it only a code 3 defect on an inspection to be fair though.
 
I doubt that the steel trunking has enough CSA to meet the requirements as a bonding conductor. It's common practice to use exposed metalwork as a bonding conductor. It's usually structural steelwork though, as that is very unlikely to be removed. I don't like the idea of using trunking as a bonding conductor, especially in a PME scenario, as if the supply neutral is lost, then the trunking would probably get warm, and possibly overheat the cables inside.
 
I doubt that the steel trunking has enough CSA to meet the requirements as a bonding conductor. It's common practice to use exposed metalwork as a bonding conductor. It's usually structural steelwork though, as that is very unlikely to be removed. I don't like the idea of using trunking as a bonding conductor, especially in a PME scenario, as if the supply neutral is lost, then the trunking would probably get warm, and possibly overheat the cables inside.

100 x 100 copper equivalent = 40.2mm and i doubt heat would be an issue in a PME scenario, no insulation.
 
He's not, Mains bond don't need to be continuous, old wive tale that one.

i cant think of a single benefit from changing a continuous conductor into a conductor interupted by containment connections thus introducing more opportunities for a break in continuity.
its certainly not what i consider an "improvement in earthing arrangements"
 
I agree that the lack of insulation will aid in heat dissapation, but if cables inside the trunking are at full capacity, and therefore at max operating temp, then I feel that a few installations worth of neutral current could cause a problem.
 
i cant think of a single benefit from changing a continuous conductor into a conductor interupted by containment connections thus introducing more opportunities for a break in continuity.
its certainly not what i consider an "improvement in earthing arrangements"


Thats exactly it ! Its only made it more likely to be broken at some point. Also the trunking is not connected to the MET other than its connection to a metal db.
 
Also the trunking is not connected to the MET other than its connection to a metal db.

well it is connected to the MET if the trunking forms part of the main bonding ?

Does the trunking earth fixing bolts have "safety electrical connection" tags that you find on pipe clamps ?
if not you can code it on that alone ;-)
 
Last edited by a moderator:
well it is connected to the MET if the trunking forms part of the main bonding ?

Does the trunking earth fixing bolts have "safety electrical connection" tags that you find on pipe clamps ?
if not you can code it on that alone ;-)


Sorry was'nt too clear with that......

It connects to the trunking instead of the MET.
 
surely bonding should from services straight to met.
less than 0.05 ohms ? doubt it

Why?

i cant think of a single benefit from changing a continuous conductor into a conductor interupted by containment connections thus introducing more opportunities for a break in continuity.
its certainly not what i consider an "improvement in earthing arrangements"

In a commercial/Industrial scenario you will find many a connection through out the length of the Main Bonding




I agree that the lack of insulation will aid in heat dissapation, but if cables inside the trunking are at full capacity, and therefore at max operating temp, then I feel that a few installations worth of neutral current could cause a problem.

And you think these conductors will be operating at Max temp with a broken pen? Will all equipment be operating under fault conditions?

Thats exactly it ! Its only made it more likely to be broken at some point. Also the trunking is not connected to the MET other than its connection to a metal db.

Well, who ever is carrying out work on any installation needs to be competent to do so, you cant design a fortress.

needs to be continous if one bonding conductor is used for two services

Say's where

Does the trunking earth fixing bolts have "safety electrical connection" tags that you find on pipe clamps ?
if not you can code it on that alone ;-)


I suggest you read the reg on that one ;)


Your the inspector, its for you to decide as to whether the installation is designed and installed correctly, Trunking can be used as Main Bonding, is it designed and installed correctly, that's your call.


 
Not on the new stuff E54, unless you don't trust what the manufactures say that is. :)

No just the one.

Always used a minimum of two, (one on each side of the butted sections) that was the norm, and as far as i'm concerned, still the norm on metal containment systems no matter what the manufacturers say. But then I suppose these days, even retaining one copper link is something of a miracle!! lol!!

Do they still call for 2 copper bonding links placed at diagonal corners across non metallic expansion joints on A/C ductwork, or has that gone by the board as well??
 
Always used a minimum of two, (one on each side of the butted sections) that was the norm, and as far as i'm concerned, still the norm on metal containment systems no matter what the manufacturers say. But then I suppose these days, even retaining one copper link is something of a miracle!! lol!!

Do they still call for 2 copper bonding links placed at diagonal corners across non metallic expansion joints on A/C ductwork, or has that gone by the board as well??

Whilst the straight sections of trunking could have a link either side, the bends and sets only have a knock out hole (usually with an earth adjacent), on the one side.
If you wanted to add another link, you would have to drill a hole, which would suggest that only the one link is deemed as being necessary.

No there doesn't appear to be a requirement for bonding across expansion joints in A/C ductwork.
 

Reply to Main bonding conductors connected to trunking. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi there, Just a quick question. Does a main protective bonding conductor require UV protection when run outside? I am under the impression that...
Replies
3
Views
647
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
This is a question (or discussion probably) regarding selecting the main earthing conductor, and subsequently the main equipotential bonding...
Replies
26
Views
6K
Hi, went to have a look at a job today, customer has had gas supply company out (for another issue) and they have commented that the protective...
Replies
1
Views
2K
Can someone sanity check my thinking please.... An 80 amp PME service head, tails to meter, 25 sq mm tails into an enclosed fused isolator with...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock