Hi Rob, thanks for this, I'm having a thick moment, and no access to GN3 where or what is the "m" in your formulae?
Rob sussed it after numerous mugs of tea, and waking up, thanks again, please ignore my request, you have my permission to put a dumb if you feel like it I won't be offended.

No need for that Pete, I should've probably added to that post.

It was just extrapolated from an article the IET published.
 
No need for that Pete, I should've probably added to that post.

It was just extrapolated from an article the IET published.
Cheers Rob, strange how the older you get, the longer it takes to get started in the mornings, bit like an old car I guess. after a few coughs and splutter you get into gear eventually.
 
Well I don't know it seems that the 0.05 ohms relates to the resistance of the banding conductor and the connection vis the Earth clamp on the pipework, it does seem quite clear from GN3 and the numerous you tube videos from respected engineers that the case involves the bonding conductor AND the earth clamp's connection to the pipework. As can be seen from the statement that the length of the Main bonding conductor has some bearing on the problem. One statement suggests that anything over 25mtrs the conductor csa should be increased, which in my eyes confirms that the resistance reading does include the bonding conductor, and not just the resistance of the pipe and the earth clamp. I do agree with some that the reading should be taken from the disconnected bonding conductor and the PIPE as described in the video that was posted earlier. Just saying.
Bad spelling? Risteard, if it's PIPE you are referring to I was merely emphasising PIPE. Sorry Mate don't know who posted "Bad spelling" just an assumption, apologies.
 
Last edited:
  1. We might consider the use of the maximum prospective earth fault current (PEFC) as a possible means of determining the length of main protective bonding conductors but this method gives an impractically low value – at least if the PEFC is taken to be 16,000A. If the conventional maximum figure for touch voltage of 50V is divided by 16,000 amps in order to obtain the maximum resistance of the bonding conductor – in order to then obtain a maximum length – we arrive at a figure of 0.003Ω.
Comparing this with the values in Table 1 shows this value to be unrealistic.

Rob, isn't the fault current limited by the supply fuse to a lower level than the measured PSCC? Would this give a better determination of the size of the main bonding conductors?
 
Rob, isn't the fault current limited by the supply fuse to a lower level than the measured PSCC? Would this give a better determination of the size of the main bonding conductors?

It would limit it yes, an you could calculate it. It wouldn't be lowered by much an the difference in conductor size would be negligible.
 

Reply to Main bonding..... yet again! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Doing a kitchen job for my daughter’s music teacher, who also happens to have been in my wife’s class at school. Nothing big… just a little...
Replies
2
Views
213
This is a question (or discussion probably) regarding selecting the main earthing conductor, and subsequently the main equipotential bonding...
Replies
26
Views
6K
Just want to know everyone’s approach to testing bonding within houses. I do a lot of EICRs, and I would say more times than not I can never get...
Replies
5
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock