Is there a reg that states the main earth bonding cable (gas,water,etc), needs to go to the MET? I've checked the regs, apart from being continuous and within 600mm of the incoming supply, I couldn't find anything specific. I've been told (by somebody with a higher pay grade), that you can run it to a sub-board. If this was the case (something which I've never done, and thought it was frowned upon), I'm assuming the requirements for the min size of the cpc supplying said DB would also have to be adequate?
 
Is there a reg that states the main earth bonding cable (gas,water,etc), needs to go to the MET? I've checked the regs, apart from being continuous and within 600mm of the incoming supply, I couldn't find anything specific. I've been told (by somebody with a higher pay grade), that you can run it to a sub-board. If this was the case (something which I've never done, and thought it was frowned upon), I'm assuming the requirements for the min size of the cpc supplying said DB would also have to be adequate?

Hi

Effectively connected to the MET is what you need to ensure. And yes however that is achieved it needs to be adequate.

Cheers
 
Yes main bonding does need to connect back to the MET, but this does not have to be a direct connection. a main bond can be connected to an EMT (earth marshalling terminal) which would then be connected back to the MET via a conductor of at least the size required for a main bond.


Sent from my iPad using Tapatalk
 
You may run main equapotetial bonding to an EMT, providing the supply cpc into that EMT is large enough to be a cpc and bonding conductor. You are correct in thinking best practice would be to run to MET but as you say it's not always possible or how another firm has installed it. If you are using an swa fed EMT you may need to check that the swa armouring is of an adequate sizing in relation to a copper conductor, what is the set up in question?
 
It was in a school where I had to install a new gas main bonding conductor (gas pipe had been moved). Managed to run it back to the MET at the origin (pain to install), only to be told later that I could of run it to a sub-board near by. The sub-board was only a 10 way, so I pretty sure the csa would of been undersized for this purpose. Was trying to find a reg detailing this for future reference, but couldn't find one. Like I said earlier, every installation I've worked in or installed the main earth bonding cables have always been run to a MET. I've installed earth reference bars but they have always been near the origin.
 
It was in a school where I had to install a new gas main bonding conductor (gas pipe had been moved). Managed to run it back to the MET at the origin (pain to install), only to be told later that I could of run it to a sub-board near by. The sub-board was only a 10 way, so I pretty sure the csa would of been undersized for this purpose. Was trying to find a reg detailing this for future reference, but couldn't find one. Like I said earlier, every installation I've worked in or installed the main earth bonding cables have always been run to a MET. I've installed earth reference bars but they have always been near the origin.

What was supplying the 10way db.? How long roughly was your run back to MET.? What size earth did you use.?
 
Let's see if I can remember......I used 16mm earth cable as the main supply tails were 35mm (junior school), the sub-board from what I can remember was 10mm T&E (4mm cpc) with no additional earth cable, the DB was about 50 or so metres away (gas bond about 5 metres from the sub-board).
 
Let's see if I can remember......I used 16mm earth cable as the main supply tails were 35mm (junior school), the sub-board from what I can remember was 10mm T&E (4mm cpc) with no additional earth cable, the DB was about 50 or so metres away (gas bond about 5 metres from the sub-board).
It wouldn't of been adequate then and you have done the correct thing.
 
Took an R2 reading using a wander lead for the cert, think it was around the 0.045 mark. Thinking about it, it was a 50m wander lead with a few turns left, so the cable run was probably around the 40m mark. But back to my original question, is there a specific reg for this as it may be handy to know if the same situation arises again in the future.
 
Max continuity resistance for an effective bonding conductor.

That it isn't.

0.05 Ohms is merely to demonstrate a negligible impedance between the connection between the main protective bonding conductor and the extraneous conductive part, i.e. you would measure between the pipework itself and the adjacent BS951 clamp to ensure that it is satisfactorily connected.

The actual resistance measured with a low-reading ohmmeter between the Main Earthing Terminal and the end of the main protective bonding conductor will be a product of its length and cross-sectional area. There is no specified maximum ohmic value for this.
 
For regulations concerning bonding conductors there is really only 543.2.1 touching on this as that states that a protective conductor (which includes bonding conductors) can be a core of a cable (and various other items), therefore a main bonding conductor can be a cable core or a single core cable. If there is a cable of suitable cross sectional area feeding a DB then this can be used as a combined bonding and circuit protective conductor.
For more information on EMT use reading guidance note 8 may assist, although as usual the advice is contradictory.
The bonding conductor should remain unbroken when looped between services (as if someone is not going to cut the cable but instead carefully disconnect the bonding clamp when wanting to randomly remove it) , but it is fine to have a bonding conductor connected to an earth marshalling terminal?
 
The bonding conductor should remain unbroken when looped between services (as if someone is not going to cut the cable but instead carefully disconnect the bonding clamp when wanting to randomly remove it) , but it is fine to have a bonding conductor connected to an earth marshalling terminal?

To be fair it is quite common for plumbers to just cut the strap holding the clamp onto the pipe and leave the clamp hanging
 
...Or the gentleman aqua director,on me pals job last week,who spun his 15mm pipe cutter on a cold water feed,by mistake,and,in my opinion,redeemed himself instantly by flattening,rolling and sealing off the geyser,with the fastest mole-grips in Manchester :wacko:
 
According to which regulation?

It is a common misconception that has no basis in any regulation.

i don't think there is a specific regulation regarding the resistance of the the cable, more of a recommendation. I've got a feeling (not to be confused with the song!), it's in guidance note 3 somewhere? It's also something that the NICIEC question during their assessments.
 

Reply to Main Earth bonding to a sub-board. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
447
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
845

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock