Large house with x2 power supplies/ service heads.

first supply 3 phase TN-S located in a pig of a place and is furthest away from the gas and water entry points and meter positions.

Second supply is a single phase TN-S located only a few meters away from the water and gas entry points to the building.

currently there is no bonding to these pipes, question is would it be wrong to use the single phase supply's MET position to main bond the water and gas?
 
can you establish (wander lead) if the 3 phase and the single phase METs are equipotential, i.e. a suitable low resistance between them. otherwise, an earth fault on the 3 phase installation would not cause a rise in potential of the extraneous metal.
 
What kind of house is this that needs 4 phases?

Is the single phase on one meter and the 3 phase on another.

Last time I cam across a setup like this was in a hotel b& b.
The 3 phase was the original supply to whole property.
The single phase was an illegal supply suposedly fitted by a western power employee for cash in hand. It had a head, meter and CU.
I only found out when I was about to call western power regarding the tails coming out the head showed evidence of overheating (burning).

The hotel owner had put most of the hotels supply on this free single phase meter. Thus overloading it.
 
I reckon,the first thing to find out,is the origin of both supplies. They may even arrive from separate sources,and the joining of MET's could cause some complications.
Have you long-leaded from the SP to the three others?
 
If the DNO were involved they would do one of two things, disconnect one supply or insist the earthing systems are physically connected together.
 
A pal of mine,has a place at Stockton Heath,which has an original underground TP+N from the roadside,TNS,to the main house,and the large garage/workshop,at the rear,has an overhead supply,with it's separate metering.
Over the years,the garage has become an extension of the property,with it's supply catering for some of the extension,and all outside lighting,etc.

Both supplies from the same DNO,and although in the past,there have been visits,regarding separate issues with both supplies,there has been no insistence,on either connection of earths,or disconnection.
 
Hi,yes,physically,and at varying distances,they do.

They do not enter any enclosure or junction box,together,but are present in the same rooms,voids and garden.

The most, any agent of the DNO has said - to my knowledge - is "....as long as any spark is aware...crack on..."

This is not the only example,of such a situation,and i myself,have left information at the incomers,to assist and prevent.

If numpties get involved....all bets are off :)
 

Reply to Main Earth Bonding (two supplies) in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening Chaps As can be seen in the attached photo , the incoming supply cable has a Earth soldered to the outer sheath of the cable suggesting...
Replies
10
Views
1K
We are refurbishing an empty commercial building at the minute and I don't do commercial stuff day in day out so not entirely clued up on...
Replies
11
Views
1K
Can a domestic consumer unit feed another consumer unit, via the Main Switch. Details are: domestic property with 100A single phase supply...
Replies
9
Views
429
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
718
Hi there, Just a quick question. Does a main protective bonding conductor require UV protection when run outside? I am under the impression that...
Replies
3
Views
674

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock