• IMPORTANT: Please note that nobody on this forum should be seeking from or providing advice to those who are not competent and / or trained and qualified in their field (local laws permitting). There is a discussion thread on this global industry-wide matter HERE. This also has more information about the warning with regards to sharing electrical advice in some countries. By using this forum you do so in agreement to this.

Discuss Main earthing Conductor also bonds water in the Electrical Forum area at ElectriciansForums.net

Welcome to ElectriciansForums.net - The American Electrical Advice Forum
Head straight to the main forums to chat by click here:   American Electrical Advice Forum

Reaction score
3
Domestic TNCS, main earthing conductor runs to water pipe, bonds via clamp with label, cable is continuous, then runs on to MET in DB.

Seems wrong, but cant find specific reg to say so....any thoughts?

Thanks,

Timotei
 
Its an earthing conductor not a main protective bonding conductor. Part 2 definitions. Fig 2.1.

But I can't see anything specifically prohibiting it.
 
I think @Wilko has it with the Ze problem. And looking at 542.4.1 (18th) it states an MET shall be provided...
and at 542.4.2 ...To facilitate measurement of the resistance of earthing arrangements...
So checking bonding requirements and Ze would be a bit of a conundrum and it could be argued unless there is separate MET complying with the former reg. then it would not comply?
 
I think @Wilko has it with the Ze problem. And looking at 542.4.1 (18th) it states an MET shall be provided...
and at 542.4.2 ...To facilitate measurement of the resistance of earthing arrangements...
So checking bonding requirements and Ze would be a bit of a conundrum and it could be argued unless there is separate MET complying with the former reg. then it would not comply?
I have agreed with you, though if the clamp to the water pipe is easily accessible and the conductor is continuous then measuring the Ze may not be a major problem. Not ideal though, I agree. I would definitely look at running in a separate conductor, just in case wet pants comes along and does some pipework alteration and decides to just cut through the cable.
 