Discuss Mains box to Consumer unit SWA or tails? in the UK Electrical Forum area at ElectriciansForums.net

its not particularly recent, But if I was to do the job today I probably wouldn't change it for metal and would record it as a departure on the EIC.
Why not metal ? You could gland straight into it
Also explain how it's a departure and not a non compliance?
It's not a consumer unit but I'd put it as a similar switch gear assembly
 
Why not metal ? You could gland straight into it
Also explain how it's a departure and not a non compliance?
It's not a consumer unit but I'd put it as a similar switch gear assembly

A departure is a non compliance, if it complied then it wouldn't be a departure.

At the time there was no suitable metal option.
Now I am still not aware of a suitable metal option, bearing in mind it is in a meter box so steel is not suitable because it will rust.
The KMF is made of a Bakelite type plastic which to the best of my knowledge is not readily combustible in the way that the soft plastic used for CUs is.
It is located outside of the building and presents no greater risk than the other plastic equipment installed in there (meter, cutout, Henley block)
 
A departure is a non compliance, if it complied then it wouldn't be a departure.

At the time there was no suitable metal option.
Now I am still not aware of a suitable metal option, bearing in mind it is in a meter box so steel is not suitable because it will rust.
The KMF is made of a Bakelite type plastic which to the best of my knowledge is not readily combustible in the way that the soft plastic used for CUs is.
It is located outside of the building and presents no greater risk than the other plastic equipment installed in there (meter, cutout, Henley block)
To depart is to install or use something that is no less safe than full compliance with bs 7671 so if bs7671 calls for non combustible enclosure on a consumer unit or similar switch gear assemblies and you don't adhere to the regulations then it's a non compliance to me and not a departure
 
Personally I feel the KMF is the wrong choice for the job in the above pics due to it having to be installed upside down as the load side is at the top..I would of opted for something different or done the job differently if nothing else would fit in the cab.

It only had to be installed upside down because I'd made off the cable and fitted the KMF the right way up before I realised my mistake.
Had I paid a bit more attention it would have been done differently the KMF would be the right way up.
 
Why not metal ? You could gland straight into it
Also explain how it's a departure and not a non compliance?
It's not a consumer unit but I'd put it as a similar switch gear assembly
If you decide to record a departure then the level of safety should not be less than obtained by compliance with the Regulations. It can be difficult to prove such things. DSs explanation in #24 does have validity that the enclosure is more likely to char than ignite but whether its level of safety is less could be debated. The only thing I would comment on if I undertook an EICR is that it is upside down :D
 
To depart is to install or use something that is no less safe than full compliance with bs 7671 so if bs7671 calls for non combustible enclosure on a consumer unit or similar switch gear assemblies and you don't adhere to the regulations then it's a non compliance to me.

Yes well as the designer I deem this departure to be no less safe than compliance with that particular regulation.
 
If you decide to record a departure then the level of safety should not be less than obtained by compliance with the Regulations. It can be difficult to prove such things. DSs explanation in #24 does have validity that the enclosure is more likely to char than ignite but whether its level of safety is less could be debated. The only thing I would comment on if I undertook an EICR is that it is upside down :D

I'd question it being upside down too, I wasn't very happy with that when I fitted it but I'd dug myself into a hole and had to get out of it.

This has got me wondering whether GRP would be considered non-combustible
 
Thinking about it further I wonder if GRP is non combustible? If so then it could be argued that it does comply.
It's a fair point.
I wonder if any tests have been carried out.
After all there's electrical equipment installed inside so would it have to have some flame retardant qualities?
 
I've put metal switch fuses in meterboxes before but used the protek ones as there not too big, gland the swa into it then gland it into the metal ccu if possible, if its in a cupboard id just bring the armoured out and go surface into the bottom of the ccu, provide a pot of white paint if the customer doesn't like the look of it :)
 
Thinking about it further I wonder if GRP is non combustible? If so then it could be argued that it does comply.
As I said in #27 it is likely to char and not propagate any flame. These materials can have differing make up some of which do have fire resistant properties.
 
It maybe argued that the meter cabinet is outside the scope of bs 7671 so can't be used in the sense of a non combustible enclosure as bs 7671 sees it, then its maybe a departure which goes back round to what dave said but only slightly different reasoning.

Anyone still listening zzzzzzzzzzzz
 

Reply to Mains box to Consumer unit SWA or tails? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
680
Hi all, Customer has an extension and this compromises existing meter position, DNO is extending incomer and putting meter box on a different...
Replies
3
Views
359
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Just wanted to know which people use. My case. Client converting attached garage into new rooms. Consumer Unit has to move to accomodate this...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock