Discuss mains leads in the Commercial Electrical Advice area at ElectriciansForums.net

Reaction score
0
Mains Leads.
I supply machines that are 21 amp per phase. the CE certification states a 2.5 5 core lead should be fitted. Which we do.
I have been asked to fit 4.0mm because the mains breakers are 32 Amp.
Isn't this the wrong way round? if the fuse was bigger it makes no sense to fit a bigger mains lead as the machine is still 21 amps per phase.
 
catch 22. 2.5mm cable is rated at 27A. that is against In < Iz, so to comply you need to eirhter reduce the In of the MCB to below 27A,or increase the cable size to be capable of carrying 32A.

only get-out might be if it's a fixed load, only needs short-circuit protection as long as there's no chance of overcurrent.
 
thanks, tectrix
The load is an electric fryer which I would class as a fixed load. it's a pandora's box of a question. the CE regs say that if the machine load is between 16 amp and 25 amps a 2.5 cable should be fitted. the fryer was tested by the CE and cenelec and if I change the leads this could infringe the certification.
However, the premises these go into have fuse boards that only do 16 or 32 amp breakers.
As you say "catch 22"
 
thanks, tectrix
The load is an electric fryer which I would class as a fixed load. it's a pandora's box of a question. the CE regs say that if the machine load is between 16 amp and 25 amps a 2.5 cable should be fitted. the fryer was tested by the CE and cenelec and if I change the leads this could infringe the certification.
However, the premises these go into have fuse boards that only do 16 or 32 amp breakers.
As you say "catch 22"
then you are OK with 2.5mm on a 32A MCB. fixed loads will nor require overcurrent protection, only short circuit protection. 433.3.
 

Reply to mains leads in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
794
I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
983
I would like to ask advice on a breaker size. Back in 2001 I turned my garage into a woodworking shop with several 240v machines. To power them I...
Replies
2
Views
1K
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock