Discuss Mains RCD tripping on larger MCB's in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
6
Hello
Looking for advise please.
Our mains RCD switch 60A 30mA MK LN 5760 is tripping when either one of my larger mcbs is turned on.
- 32A shower
- 30A sockets
- 30A cooker
I turned every breaker off and individually turned them on. All three mentioned above individually trip the mains RCD.
 
You need to understand RCDs will not trip on an overload, RCDs trip when there is an imbalance in the current flowing in the L conductor and the N conductor.
Turn ALL the cbs OFF switch the RCD ON and then switch the cbs ON 1 at a time until the RCD trips which ever cb trips the RCD would indicate a fault on that particular circuit, time to call an Electrician.
 
I would suggest that you probably have a neutral to earth fault on one of the circuits protected by that RCD and the resistance of the fault is such that the RCD will not trip until a significant current is drawn from the supply. This would account for the three different circuits all tripping the RCD. The fault could be on any circuit and only testing would determine which circuit
 
I moved into the house 2 years ago and it was there then. The issue has just started happening and means I have no electricity currently as cannot turn on sockets
The consumer unit is:
MK sentry unit
CM16
BS 5486 Pt 13
 
You need to understand RCDs will not trip on an overload, RCDs trip when there is an imbalance in the current flowing in the L conductor and the N conductor.
Turn ALL the cbs OFF switch the RCD ON and then switch the cbs ON 1 at a time until the RCD trips which ever cb trips the RCD would indicate a fault on that particular circuit, time to call an Electrician.
That's the problem, I had turned them all on 1 at a time and all three MCBs 30A+ cause the RCD to trip so difficult to identify an individual circuit problem.
 
The fault Richard suggests is a possibility, if it's the socket circuit tripping the RCD unplug everything, switch back on and try your appliances 1 by1 until the RCD trips, there is the culprit
 
Ok, I asked because I've just fixed a house with a similar situation caused by a lack of understanding in the spark who changed the consumer unit.

Could you post a picture of your consumer unit please, making sure to include the LN 5760?
 
I would suggest you follow the advice from @Pete999 and try unplugging/turning everything off that is connected to the socket circuit and then try just turning that circuit on.

If it still trips, you are going to need the assistance of an electrician and their test gear.

If you were near me, I'd come and take a peek, unfortunately Derbyshire is a bit of a drive.

Edit:- In fact regardless of whether it trips or not, I would suggest you have a look on the forums and try and find a local spark to have a look at it.
 
It might be an idea to try turning off the cooker switch near the cooker and then switching on the RCD and then the cooker MCB with everything else off and see if you still get the tripping.
With only the initial current draw from the capacitance of the circuit the RCD should not trip and I would fall back on the earlier post.
If you do still get tripping then it may be that the RCD is failing, that type is now quite old (and unfortunately difficult to get replacements).
 
I would suggest you follow the advice from @Pete999 and try unplugging/turning everything off that is connected to the socket circuit and then try just turning that circuit on.
If it still trips, you are going to need the assistance of an electrician and their test gear.

It might be an idea to try turning off the cooker switch near the cooker and then switching on the RCD and then the cooker MCB with everything else off and see if you still get the tripping.

SNAP!;)
 
Really appreciate the response I've received from this, great group.
I'll try the advise given to see if we can individually identify something.
My relative is a electrician but unfortunately in the industrial trade.
I reckon they would be willing to have a look at it for me, is there any type of tester I could advise them bring along with them.
Failing that, looks like I will be contacting a local sparky as mentioned I've noticed the RCD not easy to get a like for like now.
Thank you
 
Initially I would be considering an RCD trip test and thereafter, if that was OK, an insulation resistance test individually on each circuit.
Any electrician attending a job should have a tester to do these tests.
Sorry should have mentioned the relative in the industrial trade would probably have to borrow any test equipment needed.
Thank you for your help
 
Initially I would be considering an RCD trip test and thereafter, if that was OK, an insulation resistance test individually on each circuit.
Any electrician attending a job should have a tester to do these tests.
Sorry should have mentioned the relative in the industrial trade would probably have to borrow any test equipment needed.
Thank you for your help
 

Reply to Mains RCD tripping on larger MCB's in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
674
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
843
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock