boballum

How about this for a ponder.....
Lighting circuit wired in metal conduit buried in concrete, conduit used as the earth no seperate CPC

Replaced board reconnected conduit to main earth but readings are 45ohms obviously the conduit has broked down

My question is this, before RCD's on lighting circuits we would have rewired it but now it has an RCD with a max permissable loop of 1551ohms (roughly!) is this reading acceptable????

The circuit has class 1&2 equipment on it
 
The metal conduit is still an exposed conductive part containing live conductors and has therefore still to be properly constructed and provide good continuity throughout it's run and be earthed.
 
I agree, obviously it's not what you or the customer want to hear, but it does want sorting.

I hate that part of the job, breaking bad news to customers, you worry that they will think you're trying it on, but at the end of the day you have got to cover your arse!
 

Reply to Max loop reading using RCD in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Been looking at a CU change in a small office and would appreciate comments on the following. Office is supplied from the mains intake in the...
Replies
52
Views
6K
Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...
Replies
13
Views
2K
Just interested in peoples thinking on using the neutral through the earthing system like I came across today. I've come across many wrong...
Replies
10
Views
2K
I thought that I posted this in the DIY part of the forum but I believe I did not. I am sorry about that. I put in a 10' x 20' metal shed about...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock