Discuss Max run for 10.5 kw shower cable in the Electrical Wiring, Theories and Regulations area at ElectrciansForums.co.uk.

Thread Status:
Not open for further replies.
Please make sure you checkout our forum sponsors, many do discounts for members and, they keep the forum free to use.
  1. sidekick
    Offline

    sidekick Regular EF Member

    If 10.5 kw shower installed on 10mm t/e and 45a MCB over 15m, is it likely to have any problem as shower leaflet states max 12m run? Cable clipped direct with the exception of 2.5m running through some pipe boxing (containing hot water pipe)
     
  2. telectrix
    Offline

    telectrix Scouser and Proud of It Respected Member

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    that max. 12m may refer to 6mm. can't see a problem with 10mm. have you calculated the VD?
     
  3. sidekick
    Offline

    sidekick Regular EF Member

    just under 3v
     
  4. sidekick
    Offline

    sidekick Regular EF Member

    should any adjustment be made for the 2.5m going through the pipe box with hot pipe?
     
  5. Andy78
    Online

    Andy78 Respected Member

    Location:
    Kingston upon Hull
    This would be the area of most concern with me. How close are the pipe and the cable ? is the pipe lagged ? what's the ambient temp of the area ? etc
     
    • Like Like x 1
  6. wallyanker
    Online

    wallyanker Guest

    I know its border line but 10.5kw could potentially draw 45.7a. Maybe change the mcb to a 50a.

    10mm cable is suitable for this job
     
Loading...
Similar Threads - shower cable Forum Date
Shower supply, ever needed additional earth cable. Electrical Wiring, Theories and Regulations Mar 12, 2019
Aqualisa Quartz Electric Shower Fault - Identify Part Electrical Forum Mar 12, 2019
Thread Status:
Not open for further replies.

Share This Page

Users found this page by searching for:

  1. shower cable max length

    ,
  2. maximum 10mm cable run

    ,
  3. boxing electrical cables

    ,
  4. max power shower on 10mm cable?,
  5. whats the maximum kw shoer i can run on a 10mm cable
Electricians Directory Post a Domestic Job Post a Commercial Job