Looked in the onsite guide today as we thought we may be close to the limit of a ringmain circuit length, the guide gives out a maximum length of just over a hundred mtrs for a 2-5 / 2-5 / 1-5 ring main. Now as we are looking at a trunking system which is to be wired in singles but all at 2-5mm, does that allow extra length?
 
A ring final circuit must not serve a floor area greater than 100m2. p362
It doesn't matter what size the conductors are 2.5mm with a 1.5mm cpc or 2.5mm with a 2.5mm cpc it is the floor area that matters not cable length.
 
A ring final circuit must not serve a floor area greater than 100m2. p362
It doesn't matter what size the conductors are 2.5mm with a 1.5mm cpc or 2.5mm with a 2.5mm cpc it is the floor area that matters not cable length.

Thanks for reply but doesnt help too much, we have a longish thinnish office which we are running trunking up both sides, so floor area is not a problem, so this is commercial not domestic.
Its easier for us to run 2 circuits, there is no problem with overload as there are only about 8 dsso on each circuit feeding 8 desks with a computer and screen on each desk.

If it didn't matter about circuit length they wouldn't be published as a guide in the on site guide
 
Last edited:
Hi.

The way I calculate the maximum circuit length for a ring is this, 4 x 11.5 x 1000 / 32 / 18 = 79.9M. This assumes an Ib of 32A, but...... the current in a ring circuit will not be the same all around the ring so the way to do it is to assume 20A at the furthest point plus an additional 12A evenly distributed.

The Ib of 32 then becomes (32 + 20)/2 = 26A

So the calc is.....4 x 11.5 x 1000 / 26 / 18 = 98.3M

Where 11.5 is the max VD permitted, 26 is Ib and 18 is the mV/A/m value.

This is assuming though that Ct is 1.

So the max circuit length is 98M contained within a maximum floorspace of 100M squared.


Hope this helps.
 

Reply to Maximum circuit length in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all, My question relates to the omission of overcurrent protection (specifically overload and fault protection) at the origin of an...
Replies
6
Views
2K
Hi there, I'm Currently doing my design calcs for my college project and doing the actual Zs calculation. Formula is Zs= Ze (or Zdb) + (R1+R2)...
Replies
1
Views
1K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
421
I may have posted this before but not sure if it made it in. I want to install an EV Charger in my garage. The panel is two stories up and the...
Replies
0
Views
470
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock