Discuss Maximum demand question in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
92
A client contact me as they are getting the supply upgraded to a block of flats and UKPN need a figure adjusted for diversity for each flat.
The original contact didn’t give a crap about the supply capacity.

x6 flats have been refurbished and during this process x6 15kw electric boilers for each flat has been added. (No gas in flats).

The issue I am having is after diversity from the OSG I am getting a crazy number per flat (150a roughly) or maybe I am missing something.

With my calculations I feel I am overkill and a substation will need to be installed, how common are the electric combi boilers as they are a big problem and not accounted for by the original fit out contractors, I am close to telling client they can’t have them and need an alternative as a substation is 100k

UKPN have said you need a sub station installing if each flat consumes 150a... these bloody boilers, I suppose it’s not my problem but I want to feel I am being realistic with my advice atleast.

Each flat DB is the following:
CCT1 Boiler supply 63a
CCT2 Ring 1 32a
CCT3Ring 2 32a
CCT4 lights 1 6a
CCT5 lights 2 6a
CCT6 Oven 40a
CCT 7 Hob 16a
 
I am going by MCB with the exception of the boiler circuit as it’s 15kw on a 63a breaker.

Well at least do it properly. If there is say 5 LED pendants on that lighting circuit that could be 15w (0.07A) and you are putting that as 4A (66%).

Same for sockets. Why put through 20A for a ring final when in all honesty the installation is probably going to be half that for both rings.
 
Ifeel your pain with this, load calculations are the thing i feel least confident with. When ever i follow OSG diversity theyre always "overloaded" its then a case of rationalising to get the number down which feels like a fiddle.

Is this MCB undersized for 15kW? I get that to 65A.
 
Hi - the 15kW water boiler is a big boy and if I recall correctly we're not given any diversity allowance for heaters. Modern electric boilers can be limited to a max kW by config and manufacturers quote times for hw heating (like 6 min for 50l at 15kW and 30min at 3kW).

Can I ask what make and model is used?
 
40A looks a lot for the oven, most new ovens are pretty efficient, spec a 13A connection and and must be A or B energy rated. It would be reasonable to use that for the calcs.

The boilers are the problem, bit late now but heat pumps might have been a solution. There's a thread on the same subject here..
 
I have same problem
1st fixed 14x 1bed flats with 12kw boiler in each

I calced max demand around 72a per flat so would of thought looking at a 245kva new supply

however SSEN are saying they want to install a 130KVA supply and it will be enough

I have installed the 14x switch fuse isolators (luckily the Lewden ones come with 60 80 and 100a fuses and all sub mains are 25mm 3core

and SSEN are supplying/fitting the Ryefield

So up to them if they want a callout for a popped main head!

I have it all in writting via email so its their call now
 
I always do 100% demand of the largest load in this case the boiler then add 40% of the remainder, having applied diversity to the remaining circuits first.
 
Of corse wilko thank you.

Gabarron MAC15

I am thinking about asking a heating engineer to dial them all down to 3kw and see if they even work, that’s the only way I would feel comfortable
 
Maybe a stupid question but...

On new installs...

With the advent of low power appliances is there more sense in putting rings on 20A MCB ( mad but just for discussion, using 1.5 T&E)

On a typical install with up/down and kitchen sockets, instead of diversified 32+(32*0.4)+(32*0.4)=57.6A you have 20+(20*0.4)+(20*0.4)=36A.

Please destroy by all means but interested in the reasons why not.
 

Reply to Maximum demand question in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello everyone, I am currently in the process of estimating the electrical demand for a new construction development that will consist of an...
Replies
0
Views
802
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
632
I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
983
So, the actual job is on a farm. I think I'll keep things simple at the moment and just ask about voltage drop. I'll come on to earthing and...
Replies
11
Views
2K
Hi everyone, each leakage question here. I am needing to run some LED screens, professional type, not TVs. These are 500mm x 500mm panels and...
Replies
11
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock