We've had this discussion before, but does anyone have any idea what load can be put through a double socket?

The socket in question is an MK logicplus, installed in a commercial kitchen. The supply cable is 6mm, converted from a previous cooker circuit to a double socket. (information gathered from staff working there, I don't know the rating of the OCPD, but I bet its still whatever the cooker needed, not downgraded for a socket on a radial)
One socket has a deep fat fryer plugged in at 3kW, and the other is either a toaster, kettle or whatever else is needed.
There is another identical fryer in the kitchen, but it is off the rfc. They would like the 2 fryers in the same area of the kitchen, hopefully off the same double socket.
So 3kW full on is over 12A … 2 of them, 24, 25A?
Obviously, cooking with the fryers there will be diversity, and they wont be on full, but can a double socket cope with 24A for any length of time?

Hypothetically, if this double socket was a spur off an rfc, would a 2.5mm T&E supplying the double socket cope with the load?

Maybe manufacturers need to print it on the front of the socket?
13A per outlet, 20A between both outlets if it is a problem
 
As far as I know the British standard requires a twin socket to handle 20A.

Feeding two loads like this through a twin socket is far from ideal, though it would probably work ok.
 
The OCPD doesn’t need to be downgraded from what the cooker needed, it is only protecting the cable and the 13A plugs have their own protection.
true, but as the socket/load has protection of 2 x 13A BS1362 fuses, it may be beneficial to downrate the OCPD to 20A. this would comply with the recommendation of a 20A load on a double socket outlet. the down side would be probable nuisance tripping.
 
The OCPD may very well already be downrated, but knowing the state of the place, it probably isn't.

I was doing PAT reports in the building (see I didn't call it PAT testing;))
and I've come across a few instant fails on visual inspection.

2 examples - outside fairy lights in the beer garden.

1. Proper IP rated 2 gang outside socket... all good so far, grey T&E into plugtop :eek:, then connected to old festoon lighting with connectors wrapped in duct tape:confused:. Roughly clipped to wooden fence.

2. From the same socket, plugtop and T&E:mad: around the other fence to an old metal coffee tin screwed to the wood. 20mm hole in side of tin, pointing downwards at least, with a grommit. Inside the tin is a standard metalclad socket. From here the actual fairy lights are plugged in. (the lights themselves passed;))

And no... the coffee tin isn't bonded to anything.


Back to the fryers

The running load is probably less than the full 3kW... maybe full until the oil heats up, but put down a little depending on what's cooking.
 
And don't forget 'PAT' is still not the correct term.
 
The OCPD may very well already be downrated, but knowing the state of the place, it probably isn't.

I was doing PAT reports in the building (see I didn't call it PAT testing;))
and I've come across a few instant fails on visual inspection.

2 examples - outside fairy lights in the beer garden.

1. Proper IP rated 2 gang outside socket... all good so far, grey T&E into plugtop :eek:, then connected to old festoon lighting with connectors wrapped in duct tape:confused:. Roughly clipped to wooden fence.

2. From the same socket, plugtop and T&E:mad: around the other fence to an old metal coffee tin screwed to the wood. 20mm hole in side of tin, pointing downwards at least, with a grommit. Inside the tin is a standard metalclad socket. From here the actual fairy lights are plugged in. (the lights themselves passed;))

And no... the coffee tin isn't bonded to anything.


Back to the fryers

The running load is probably less than the full 3kW... maybe full until the oil heats up, but put down a little depending on what's cooking.
Your para 1), got to be a joke hasn't it? never read the whole post, please ignore.
 
I had a tenant who plugged to 3kw heaters into a MK outside plug and it melted it! They heaters were probably both on full tilt constantly but IMHO it's not going to end well with the fryers if they are both turned on together.
 

Reply to Maximum load across both sockets of a double socket in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
806
Pub kitchen I was doing PAT for, opening at 12 today. They have had to reconfigure where everything sits, so new location for double deep fat...
Replies
19
Views
3K
Hello. I'm in the UK, and have some questions/concerns about my kitchen set up. So the fuse box has 4 breakers/circuits for the kitchen (the...
Replies
6
Views
1K
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
710
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock