Discuss Maximum Zs for distribution circuits protected by 60947-2 MCCB's in the UK Electrical Forum area at ElectriciansForums.net

Usually the manufacturers have online details as MCCB can have different adjustable setting so no one answer fits all, a chat to technical can also get the info unless you provide us with more details.
 
I'm carrying out a EICR on a large factory with many distribution circuits, meaning that I will be dealing with multiple different scenario's with regards to device setting and cable size etc. So calling technical every time may not be ideal.
 
I'm carrying out a EICR on a large factory with many distribution circuits, meaning that I will be dealing with multiple different scenario's with regards to device setting and cable size etc. So calling technical every time may not be ideal.

It's pretty much your only option to be accurate with the manufacturer's stated values. There are no all encompassing figures such as the BS7671 info that exists for other devices.
 
You make a list and call them once or find a website with the values listed, without you giving us a brand we can't really guide you any better as their are many makes and models and not all have readily available charts. The distribution power panels in factories usually are a common brand through out, although not always the case so if you can get the make and generation of the device we might be able to help.
 
I'm carrying out a EICR on a large factory with many distribution circuits, meaning that I will be dealing with multiple different scenario's with regards to device setting and cable size etc. So calling technical every time may not be ideal.

There should be detailed information to hand with regards deisign, MCCBs are not for ordinary use.

Cheers
 
No excuse Dave, if this is a large factory i'd be advising them of their legal duties. Many factors to consider discrimination etc.

Cheers

I'm sure we all can and would advise them of such. It doesn't help the poor bloke on the ground trying to carry out testing on an installation which doesn't have the paperwork it should have
 
No Dave, its little help. He will have to dig into his design knowledge, they wont want the light going out.Hopefullt they will give him the scope rquired.

Cheers
 
Thanks for the replies gents. All the boards are Merlin Gerin/Schneider. I have been given a huge number of files from the original building handover but typically it contains zero information with regards to the original electrical installation.

I shall ring those lovely people at Schneider when I have all the DB schedules completed.
 
Thanks for the replies gents. All the boards are Merlin Gerin/Schneider. I have been given a huge number of files from the original building handover but typically it contains zero information with regards to the original electrical installation.

I shall ring those lovely people at Schneider when I have all the DB schedules completed.
be very careful when you call schneider.

honestly they still work as seperate companies with there own structure somewhat within schneider.

if you call the wrong place you might be talking to someone that only knows about square d etc.

the schneider office in telford would be a good place to start, im sure the mccb stuff we had was ordered through telford branch (we were working at ashby branch aka andover controls/tac)

this is the one google throws up but it could be wrong

0870 608 8608
 
Last edited:
be very careful when you call schneider.

honestly they still work as seperate companies with there own structure somewhat within schneider.

if you call the wrong place you might be talking to someone that only knows about square d etc.

the schneider office in telford would be a good place to start, im sure the mccb stuff we had was ordered through telford branch (we were working at ashby branch aka andover controls/tac)

this is the one google throws up but it could be wrong

0870 608 8608

Thanks Shanky,

I have had the above issue before with them, I just ask for Merlin Gerin technical support usually.
 

Reply to Maximum Zs for distribution circuits protected by 60947-2 MCCB's in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Does a RCBO protecting a single circuit mean it can have a maximum Zs of 1667 Ohms since it's being used as fault protection?
Replies
3
Views
3K
Does anyone know where I can find the maximum Zs values for AFDD's? Table 41.3 refers to 60898 and 61009-1 but AFDD's are BS 62606
Replies
4
Views
5K
Evening all, Been to a job on Fri where the customer had a condition report completed. Two of the remedial identified was that there were too...
Replies
7
Views
1K
Hi Guy's, I'm revising for my 18th amd 2 and came across a question that has me a little confused. I think its probably the question is badly...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock