What are peoples thoughts.

From the BYB

“Circuit-breakers and RCDs are primarily circuit-protective devices and, as such, they are not intended for frequent load switching. Infrequent switching of circuit-breakers on-load is admissible for the purposes of isolation or emergency switching. For a more frequent duty, the number of operations and load characteristics according to the manufacturer’s instructions should be taken into account or an alternative device from those listed as suitable for functional switching in Table 53.4 should be employed.”

Are there any MCBs out there where the manufacturer approves their use as functional switches. The few I've read up on don't recommend it.

Had a few MCBs fail where being used as functional switches and would like to rewire via a grid switch arrangement. I just don't like the idea of shop workers going in and out of a DB at will, the door no longer closes and it just don't sit well.

Are there any other points that could strengthen the argument to do this or am I being a bit picky?
 
We used to do work for a major retail chain and this was common practice. The boards were generally Crabtree C50 and the mcbs had colour coded discs fixed below them to indicate the time they should be switched on. So for early morning stock and cleaning work you would switch one colour on to give partial lighting. Some had been operated so many times the toggles were floppy and it is debatable whether the devices would operate under fault conditions.
 
Common practice with shops is to wire the circuits to be switched via a contactor to a keyswitch by the door, then the shop workers come in, operate the keyswitch and everything is ready to go. Upon leaving they do the same in reverse and all the circuits which need to be turned off turn off in one go, leaving anything like alarms, fridges or computers left on. That way they don't need to touch the distribution board and there is less scope for things being turned off which shouldn't.
 

Reply to MCB as functional switches?? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
676
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
789
Hi everyone I bought the following device for the purpose of inspection and testing of DPs and its connecions...
Replies
7
Views
710
Hi all, Been browsing these forums for a while, always great to learn a new way to skin the same cat. Anyway, cut a long story short, was an...
Replies
11
Views
578
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock