Posting a message to the forum will remove the above advertisement
  1. This site uses cookies. By continuing to use this site, you are agreeing to our use of cookies. Learn More.

Discuss MCB then RCD in the Commercial Electrical Talk area at ElectrciansForums.co.uk.

Thread Status:
Not open for further replies.
Please make sure you checkout our forum sponsors, many do discounts for members and, they keep the forum free to use.
  1. peeko
    Offline

    peeko EF Member

    Location:
    Derby
    Business Name:
    Peeko
    Hi everyone, hope you can help

    Recently we've completed an EICR on a commercial property and it's thrown up some issues with the lighting. The installation method is rough as, T&E just chucked on top of the ceiling tiles as we've all seen a million times before so we'll be sorting this as part of the remedial works.

    One of the issues I have is that I'm not convinced from looking at the state of it is that the cables in the walls/partitions of the office areas have the adequate 50mm protection/are inside metal conduit, therefore as per amendment 3 I've got to provide RCD protection to the circuit.

    The circuits come off an old Square D 3 phase DB, and if anyone has had the misfortune to look for RCBO's that fit these, they'll tell you they're hard to get hold of and cost a small fortune. My idea is this - adequately protected cable from the current MCB to a separate enclosure of double pole RCD's, which then provide protection to each lighting circuit.

    I've been told this is OK, just wondered if anybody has experience of this, pro's/con's etc? Obviously in an ideal world I'd swap the board for something more modern with RCBO's that are available/not a fortune, but for a couple of circuits I don't think they'd go with the cost of this, maybe down the line as they make alterations.

    Thanks in advance
    Charlie
     
  2. hightower
    Offline

    hightower Guest

    Sounds like a plan to me, people often do this in domestic for new shower circuits etc.

    Only thing I'd say about it is make it bloody obvious that there's a protection device after the MCB - if somebody on site needs to reset it, they may not know it's related if it's not obvious to them.

    P.S. Isn't this a bit above the remit of a PAT Tester? ;)
     
    • Like Like x 1
  3. stantheman
    Offline

    stantheman Regular EF Member

    How old is the installation?
     
  4. Andy78
    Online

    Andy78 Respected Member

    Location:
    Kingston upon Hull
    Have you tried Schneider for a compatible rcbo ?
     
  5. peeko
    Offline

    peeko EF Member

    Location:
    Derby
    Business Name:
    Peeko
    :p very much above the remit of a PAT tester!

    Won't be attempting myself - our sparks will be installing/testing/cert-ing, just like to make sure they're not bull****ing me at times, especially when it's a scenario I've not seen before.

    Installation is about 35-40 yrs old
     
    • Like Like x 1
  6. peeko
    Offline

    peeko EF Member

    Location:
    Derby
    Business Name:
    Peeko
    Hi Andy, they sent me 2 part codes - however every site I check says they're discontinued, not keen on putting used in off fleabay
     
  7. stantheman
    Offline

    stantheman Regular EF Member

    "One of the issues I have is that I'm not convinced from looking at the state of it is that the cables in the walls/partitions of the office areas have the adequate 50mm protection/are inside metal conduit, therefore as per amendment 3 I've got to provide RCD protection to the circuit"


    Has the client requested the code 3 work?
     
    • Like Like x 1
  8. peeko
    Offline

    peeko EF Member

    Location:
    Derby
    Business Name:
    Peeko
    Hi Stan - yes 2 quotes, one C2s, one for C3s. Last time we did work there they did all.
     
    • Like Like x 2
  9. Andy78
    Online

    Andy78 Respected Member

    Location:
    Kingston upon Hull
    I would persist with that one. Last schneider rcbos I used in a square d tpn board was only a couple of years ago.
     
  10. peeko
    Offline

    peeko EF Member

    Location:
    Derby
    Business Name:
    Peeko
    Thanks Andy, I'll have another look, might be a case of ringing round to see if anyone has any surplus stock gathering dust
     
  11. Jay Sparks
    Offline

    Jay Sparks Forum Mentor

    Location:
    Bratford
    You could even ask about on here. Start a thread and see if any members have any kicking about, like you say, gathering dust. Not sure what part of the forum you would be best putting in though.

    Jay
     
    • Like Like x 1
  12. Andy78
    Online

    Andy78 Respected Member

    Location:
    Kingston upon Hull
    What series are the old Square D and what serial numbers have schneider provided you with ?
     
  13. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Staff Member Moderator

    Location:
    Northamptonshire
    Schneider rcbos are readily available for Square D KQ boards. I am not so sure, if it is a QOE board that they are compatible but I could be wrong.
     
    • Like Like x 1
  14. Sam cook
    Offline

    Sam cook Sparkyboysam

    Location:
    Kent
    I've just recently fitted Schneider KQE RCbo Devices In a square d push fit bus bar 3 phase Board. Funny really about five years ago I sold a load of square d rcbos becaue couldn't see me using them and already go ample stock of MCB and rcbo devices. My wholesaler holds them for me. Some say ironic at what the Schneider cost in region of 50-60 quid.
     
Thread Status:
Not open for further replies.

Share This Page

Electricians Directory Post a Domestic Job Post a Commercial Job