Discuss MCCB with RCD settings in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
51
MCCB with RCD bolt on, anyone know how to work these settings out? Ignore settings now but this is upfront RCD TT system so I want to top one to be 0.3 for 300mA but unsure on bottom?

4A051DE4-A81E-4B35-991F-3E4D76F0AB6F.jpeg


016B9063-754D-4364-9371-214F7D6C5946.jpeg
 
I not sure I understand the question. You do realise that the time setting on the device is marked in seconds, and so you need to convert milliseconds to seconds?
 
As a matter of interest, why does it need to be changed?
It was left on 0.1 so 100mA and was nuisance tripping, hench I’ve changed to 300mA
Is the question, what is the appropriate time delay setting for the installation?

The minimum that doesn't cause a nuisance and at or below the reg requirement or customers spec.
Yes that was all, couldn’t find anything online I knew how to set current just the time
 
So does that acheive disconnection times satisfactorily now that you have changed it to 3 x the original ma? Is it not the case if it is tripping that some investigation may be due? Maybe IR tests if it is possible?
 
That is commonly called a vigi module. You will notice when set for 30ma there is a line down indicating to set to no delay so additional rcd protection is provided.
 
So does that acheive disconnection times satisfactorily now that you have changed it to 3 x the original ma? Is it not the case if it is tripping that some investigation may be due? Maybe IR tests if it is possible?
Yes all sub circuits and feed from mains all tested fine with IR, now set to 300mA it’s all fine there’s discrimaination now 300mA to 100mA and so on, just didn’t understand the bottom dial
 
So does that acheive disconnection times satisfactorily now that you have changed it to 3 x the original ma? Is it not the case if it is tripping that some investigation may be due? Maybe IR tests if it is possible?
Yes all sub circuits and feed from mains all tested fine with IR, now set to 300mA it’s all fine there’s discrimaination now 300mA to 100mA and so on, just didn’t understand the bottom dial
 

Reply to MCCB with RCD settings in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

We are looking for a distribution board to provide 3 * 160A three-phase feeds, but they are basically redundant supply path options so max total...
Replies
4
Views
285
Evening everyone… I’ve attached pictures for your leisure.. so basically the customer does not have any RCD protection.. 3036 fuseboard is in...
Replies
9
Views
332
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
780
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
Hello All. New here and will be flooding with terrible questions for my own knowledge. Just trying to learn so some questions like this maybe very...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock