Discuss MCS requirements For off grid PV in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

J

jules27

Hi there ,
Just a quick one can anyone point in the direction of what is required under to MCS to get FITs for off grid installs ?

Also Are there any places that can be recomeded for reasonably priced dc isolators (wanted a 40-60a one )

Thanks
 
The main requirement that causes problems is the need to fit an accredited total generation meter - as only 230V ac are available, and this needs to only meter the output from the PV. So if there is some other method of charging the batteries, apart from PV panels such as a back-up diesel generator, then this will be an issue that needs to be resolved in the design of the system. i.e.

pv--
inverter--
meter--
battery charger/controller--
batteries--
load
|
generator

And here you obviously cannot use a grid-tie inverter.

All the other relevant DTI Guide and BS7671 standards will still apply.

The owner is required to sign a declaration every year to confirm that the power produced is actually used and not just dumped.
 
Last edited by a moderator:
@TedM

Now, if this system would be connected to a dwelling house, as opposed to sitting in a field connected to a transformer up a pole, if it was say 3.6kWp, for FiTs is it classed as <4kWp (even though no MPAN bering in mind the wording in the secription of 'site') or would it be 'stand-alone'.

As I understood it stand-alone, meant a system desgined purely for the puposes of generating electricity as opposed to something designed for loacl consumption, hence the 'connection to an occupied building'
 
Thanks for the replies , sorry been really busy, I was thinking of a dwelling with panels ,but does n't seem much point at that rate ! still I'm intersted in now its done , as per BS7671.... but I dont know about the DTI guide ?
 
An off-grid system feeding a dwelling get the full rate. Stand-alone applies when there is no dwelling.

MPAN is just one of the several criteria for determining whether you have just one or multiple 'sites'. Lack of an MPAN doesn't mean you must be stand-alone.
 

Reply to MCS requirements For off grid PV in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

hi thank you for help in advance have a potential pv installation for a garage roof that is some 60m from the main house (main incomer in the...
Replies
9
Views
2K
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
741
I currently have a 3Kwh solar PV system which was installed over 12 years ago and getting a very good FIT payment and I don't want to lose it! I'm...
Replies
0
Views
4K
Hi, Similar'ish question to my other thread but little more info now so a different approach but sorry if duplication. UK, single phase. Just had...
Replies
0
Views
1K
Just hoping to pick someones brain here: Customer has an existing off grid PV install to a barn He is now building a house on the site (this will...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock