spud1

-
Arms
Reaction score
55
Hi again!

Which value is best to record in a certificate or report, a max measured or a calculated Zs?

I know Sparkies who do it both ways, but personally I take measured values at all the points of utilization to find the highest, then I calculate Ze+(my highest R1+R2) for the circuit and then I compare the max measured and my calculated values and record the highest of the two on the certificate.

Any thoughts?
 
If safe to measure Zs and I've measured it, I put the highest measured value down. If not safe to measure, I calculate it from Zdb + (R1+R2).

Edit: if it's a TT system and (for example) Ra = 100Ω and the board is at the origin (so Ze = 100Ω ish) but Zdb goes down to, say, 20Ω once bonding is connected, I would use Zs = 20 + (R1+R2).

(tin hat on)
 
If safe to measure Zs and I've measured it, I put the highest measured value down. If not safe to measure, I calculate it from Zdb + (R1+R2).

Edit: if it's a TT system and (for example) Ra = 100Ω and the board is at the origin (so Ze = 100Ω ish) but Zdb goes down to, say, 20Ω once bonding is connected, I would use Zs = 20 + (R1+R2).

(tin hat on)
But would a calculated value not be a truer reflection of the circuits prospective max Zs i.e. with no parallel paths at play
 
Yes, hence the tin hat. :)

In the example of a TT system, though - unless you're using a 300mA or 500mA RCD for fault protection, it's not going to make much difference.

Bonding should be in place for ADS. When you measure Zs, bonding is in place.

If you measure Zs for some circuits (sockets, say), with values all around the 20-odd ohms mark, and you decide to use "proper" Ze + (R1+R2) for those you calculate Zs for, they'd be around the 100-odd ohms mark, and it would look... odd. You'd not really be comparing like for like (between circuits).
 
Yes, hence the tin hat. :)

In the example of a TT system, though - unless you're using a 300mA or 500mA RCD for fault protection, it's not going to make much difference.

Bonding should be in place for ADS. When you measure Zs, bonding is in place.

If you measure Zs for some circuits (sockets, say), with values all around the 20-odd ohms mark, and you decide to use "proper" Ze + (R1+R2) for those you calculate Zs for, they'd be around the 100-odd ohms mark, and it would look... odd. You'd not really be comparing like for like (between circuits).
In your TT example the highest reading would always be the calculated value so that would be method I would use for all circuits, so I would be comparing like for like wouldn't I?

Also with regards to your comment on bonding, what would happen if the utility pipe were upgraded to plastic and the parallel path previously giving you 20 ohms disappeared?

Oops I havent got a tin hat!:(
 
Yes, these are points I had thought of, and you're right (I almost added a "PS" along those lines but assumed you would respond as you have).

If, ultimately, the presence or absence of bonding would make a difference between requirements for ADS being met or not (let's say fault protection for a particular circuit is via a 500mA RCD only, and Ra>100Ω, but with bonding Zdb is <<100Ω) then this would require a different response, depending on whether it's a new installation or an inspection and test.
 
At the end of the day, make a note on the test sheet to say what you've done, then it's clear for whoever reads it in the future. :)
 
Hi again!

Which value is best to record in a certificate or report, a max measured or a calculated Zs?

I know Sparkies who do it both ways, but personally I take measured values at all the points of utilization to find the highest, then I calculate Ze+(my highest R1+R2) for the circuit and then I compare the max measured and my calculated values and record the highest of the two on the certificate.

Any thoughts?
Measured.
It’s a schedule of test results, not a schedule of calculations.
 
Record the measured value. One of the reasons we record the values is so that subsequent EICRs and other testing can be compared to the original test results to track any deterioration in the circuits.
But wouldn't any deterioration in the circuit be identifiable in the compared R1+R2 measured readings?
 
8A44D91E-4715-4503-8ECE-C8B568E9B401.pngFor initial verification The regulations say that where the effectiveness of the protective measure has been confirmed at a point located downstream of an rcd the protection of the installation downstream from this point may be proved by confirmation of the continuity of the protective conductors.
An R1+R2 test confirms this.
Where the rcd is tested and satisfies fault or additional protection then further testing is not nessicary according to the above NICEIC tech article.
If there’s no rcd and the circuit relys upon an ocpd for fault protection then the zs shall be confirmed by the appropriate measures.
643.7.1

Take it how you will I’d still just calculate or measure the Zs personally and write it in the appropriate column on the schedule of test results
A controversial point maybe?
 
Last edited:
See, I don’t understand this urge to fill in all the boxes?
The whole point of the schedule is to record the values obtained from tests, that you’ve conducted (hence the name).
You don’t get a gold star or a Brucie Bonus for filling in all the boxes. Unless of course you calculate the R2.

The other thing is, on some circuits the measured value for Zs will be considerably lower than the calculated value due to parallel paths.
For instance, boiler circuits or immersion heater circuits, all those copper pipes and bonding conductors will lower the Zs.
 
My recollection from the 2391 is that zs should be measured when safe to do so and calculated otherwise.

The interpretation was that sockets would be measured using an adaptor. Pretty much everything else calculated.
 
Don’t know what the current version of GN3 advises, but my old copy says that a Zs test at socket-outlets and at exposed conductive-parts of equipment on other circuits, is sufficient to confirm continuity of the CPCs. That’s for periodic inspections.
 
Both work in conjunction with each other, all sparks should use both, the calculation proves what the Zs should be without any parallel paths if there is any, it also shows if the maximum permissible Zs could be exceeded, but this doesn’t give proof of the earth loop so the test is required.
The test proves you have an earth loop, if it’s lower than expected it’s likely there are other earth paths and if it’s higher than expected then this indicates a problem.
Only doing the calculation is to me just a bit lazy and potentially very dangerous
 

Reply to Measure or calculate your Zs? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K
So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Replies
3
Views
1K
Hi, I did my first EICR on a TT system today and the Zs was a lot higher than Ze+R1+R2 on everything. Zs was around 3.5 ohms on all of the ring...
Replies
10
Views
989
OLDBOY
O
Got my am2 coming up on Tuesday and I know I have to calculate my Zs readings Maybe I’m overthinking this but am not sure if I need to use the Ze...
Replies
17
Views
3K
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
861

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock