Hello guys.

This isn't a job, just so that you know. Just exploring.

I have a couple of AC motors and I am playing with them. One of the things I want to do is measure the current draw.

So I attach them to a power source and switch it on and off they go doing their thing. No problem there.

So I then switch them off and insert a multi in the line, set it to AC amps and switch it on again and motor doesn't operate. I do get a reading on the meter but it's not what I expect it to be.

Here's an example:

35W 50Hz 230V, although actual supply is 240VAC. This is from a dishwasher. It's the drain pump. Of course when I power it up on the bench it's not pumping water so it's not under load.

Anyway, here's the calculation:

Current i amperes = 34W / 240VAC = 0.142 amperes. Or 142 milliamps.

I would expect the measured current to be less than that given that i's not actually pumping water. Right?

So I insert the meter into the circuit and:

Set it to AC Amps I get a reading of 9.9

Set it to AC milliamps I get a reading of 59.8 milliamps
Now that's a possibility, I guess, since it's not under load.

I should point out that I only have two digits before the decimal point on this meter when in milliamp mode.

I didn't bother with microamps mode.

And, btw, the motor doesn't run while the meter in in the circuit. Runs fine when I remove it. Why would that be? Is the resistance of the meter that much that it reduces the current to the extent that the motor no longer functions? That would seem odd to me.

Can anyone offer any suggestions as to what's going on here?

How could these values be so wide of what I am expecting?

Appreciate your input.

Thanks
 
use a clamp meter instead. you need one with a resolution low enough.e.g. 1mA.
 
Hello guys.

This isn't a job, just so that you know. Just exploring.

I have a couple of AC motors and I am playing with them. One of the things I want to do is measure the current draw.

So I attach them to a power source and switch it on and off they go doing their thing. No problem there.

So I then switch them off and insert a multi in the line, set it to AC amps and switch it on again and motor doesn't operate. I do get a reading on the meter but it's not what I expect it to be.

Here's an example:

35W 50Hz 230V, although actual supply is 240VAC. This is from a dishwasher. It's the drain pump. Of course when I power it up on the bench it's not pumping water so it's not under load.

Anyway, here's the calculation:

Current i amperes = 34W / 240VAC = 0.142 amperes. Or 142 milliamps.

I would expect the measured current to be less than that given that i's not actually pumping water. Right?

So I insert the meter into the circuit and:

Set it to AC Amps I get a reading of 9.9

Set it to AC milliamps I get a reading of 59.8 milliamps
Now that's a possibility, I guess, since it's not under load.

I should point out that I only have two digits before the decimal point on this meter when in milliamp mode.

I didn't bother with microamps mode.

And, btw, the motor doesn't run while the meter in in the circuit. Runs fine when I remove it. Why would that be? Is the resistance of the meter that much that it reduces the current to the extent that the motor no longer functions? That would seem odd to me.

Can anyone offer any suggestions as to what's going on here?

How could these values be so wide of what I am expecting?

Appreciate your input.

Thanks
Use a clamp on meter as Tel said with a low scale
 
As Matthew says, don't expect a cheap clamp meter to be anywhere near accurate enough to read low mA figures.
 
You don't need a clamp meter, multimeter is fine. Have you got the meter leads in the right sockets i.e. A and COM? If you have, then there's no circuit through the meter so either the shunt or the fuse is dead. But with a dead fuse I wouldn't expect a reading, and I've never managed to blow a shunt. If you have accidentally left the red lead in the V socket the pump won't run and you'll get a nonsense reading.

BTW the current won't be P/V because of the power factor, and running the pump dry will ruin the seal.
 

Reply to Measuring current draw by AC motor. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi Forum Members I have a 4 pole single phase 240VAC 315 watt motor from a central heating heating system that I think is bad. It's the room fan...
Replies
18
Views
2K
Hi. I've read much about ac vs dc but can't find a 'simple' answer. If current alternates 50 times per second in a uk mains circuit, why do live...
Replies
23
Views
1K
Hi, First of all I must explain why my posting came to be on this site, I was looking on the internet for a forum that could help with a project...
Replies
8
Views
1K
I have a pressure washer that I got as part of "a good deal", actually an exceedingly good deal as I later found out. I've had it a while, I guess...
Replies
5
Views
1K
Hi everyone :) my first post here. Quick background I'm a newly qualified installer of somewhat advanced years whose just starting out in the...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock