Discuss Medical Centre in the UK Electrical Forum area at ElectriciansForums.net

vini

-
Reaction score
13
I had a customer (doctors) whose DB has an ELCB main switch which tripped over night causeing a fridge which is plugged into the ring main to be off and ruined various vaccines. Is there any way to have the fridge isolated from the ring main and ELCB other than install a garage unit RCD for the fridge on a single socket?

It may be a one off that the ELCB tripped but it costs hundreds of pounds to lose the fridge. Do any of you have experiences in ensuring electrical supplies are continued for medical situations?
 
a dedicated socket for the fridge can be installed without RCD protection as long as you run in surface cable. ( or if buried cables, enclose or protect as per 522.6.101.)
 
Unfortunately the ELCB is the main switch on the DB so if I branched off from the supply side of DB, the only protection is a 100A electricity suppliers fuse.
 
Wouldn't be connecting off live side of existing board. Best way is to replace existing with either a board with rcbos or a dual rcd high integrity board and install a new non rcd identified socket, wired surface so cable is not concealed.
 
Reg 411.3.3 allows another exception (no rcd) with a documented risk assessment, but I'd expect the previous suggestion is easier to achieve.
If it is a GP surgery, surely they should be considering their existing install in any case?
 
Last edited:
Reg 411.3.3 allows the another exception (no rcd) with a documented risk assessment, but I'd expect the previous suggestion is easier to achieve.
If it is a GP surgery, surely they should be considering their existing install in any case?
especially now that the NHS have told them to bin their socket covers. :mad:
 
In a surgery I visit a gu10 has been hanging out of the fitting for around two years now! I assume they have lost the clip lol. The lamp is still working too.
 

Reply to Medical Centre in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Woke up this morning and tried to turn on the computer (work from home) wouldn't power on, checked lights they worked fine. Went downstairs to...
Replies
21
Views
2K
Hello, So I noticed my fridge had lost power, disconnected it and tried a hoover in the same socket and this also wouldn't work. I tried the...
Replies
1
Views
822
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
540
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
779

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock