Discuss medical locations query in the Commercial Electrical Advice area at ElectriciansForums.net

Reaction score
15
excuse the paraphrasing .I'm trying to figure out if lighting circuits in group 1 /2 locations HAVE to be on rcd.or if it depends on...eg...unprotected cables in a metal stud wall ...or if it is in a room containing shower
710.411.3.2.5 says ..in medical locations of group 1 & group 2...WHERE rcds are required only type A or B (not type AC) shall be selected..
then
710.411.4..TN systems says ..In final circuits (which presumably would include lighting ?)of group 1 rated up to 63 amp rcds SHALL be used
then
next paragraph says in medical locations of group 2 rcds shall ONLY be used for operating tables X rays etc.
it just sounds a bit conflicting to me...or maybe just too late at night to think clearly.
 
Hi - I'm not expert on medical locations, but this is my take :

710.411.3.2.1 : confirm if you are in room designated in gp 1 or 2 (where tripping itself causes a hazard as it interrupts a medical procedure). If so, then AC type RCD shall not be used. But type A or B (best in my view) may be used.
710.411.3.3 : confirm if your room uses IT system, if so additional protection by an RCD shall not be used.
710.411.4 : if TN used, use RCD spec from 415.1.1 (but type A or B) . Note the list of circuits is not exhaustive but it specifies some that are compulsory.
710.411.5 : if TT used, refer to 710.411.4

So I think for a non IT medical location 1 or 2 we should provide additional protection using RCD type B for lighting if required due to the usual cables in walls etc. Also lights are likely required to be emergency type.

I'm sure some more experienced heads will help out :)
 

Reply to medical locations query in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

I am looking at installation of an architectural dimmer, that is will supply 6 channels, with 20A circuits each (2400W ea). Our hall has can light...
Replies
2
Views
670
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
I've started to move over to AMD 2 forms for my CU installs, if only because the schedule is so much easier to tick and I can stop sticking labels...
Replies
4
Views
1K
Hi all, Got an antique light fitting that for some reason she wants putting up (can't say I love it haha) however it didn't come with any...
Replies
9
Views
3K
Hi Everyone Thank you for accepting me into this group. I'm obvoiusly new to this forum so please excuse any mistakes untill I familiarise myself...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock