Discuss megger 1552 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

R

Ross Trician

Hello all, I am after some advice,

I have just bought a megger 1552 tester. I was "practicing" with it today as I am a novice when it come to inspection and testing. I found the instruction manual a bit naff. I was trying to do a Zs/earth fault loop impedance on a radial circuit and the meter kept saying "trip" the way I interprited using the meter is it can use a 2 lead rather than a 3 lead test but shows trip. if I also put the black lead to neutral it gives a reading.

could someone please give me some clarity on the method or what I am doing wrong.

Any help would be appreciated.

Ross.
 
presumably you are on 'no trip loop'

on the side of the meter, there is a black hole at the bottom with 'no trip loop' written on it.

it does what it says on the tin!

if you are set to 'no trip loop' for EFLI or PFC then you must puit your black lead in the no trip loop hole and connect it to the neutral of the circuit you are measuring

you will find as well, if you were measuring Ze using no trip loop you DONT disconnect the main earth!

its just the way it is......have fun now

and test safely!;)
 
Thanks for the quick reply Shakey.

I would of thought the instructions that come with the tester would be a bit beter than what they are. I have been an electrician for a good few years but not familiar with the inspection and testing side of things. do you have experience with the megger meter? if so whats your opinions etc of it,,

Cheers Ross.
 
yeah, got lots of them, very very experienced with the meter

simple to use, but a bit slow on the no-trip functions

but like you have discovered, the manual is useless, and i badgered Megger into supllying me with the plug top lead with the three connectors on (so you can do the ring cross connects) for free

it hacks me off the way they want you to buy extras

bought a few PAT testers off thwem, and the 'extras' were going to be over 150 quid per meter on top!!!

I say 'were' cause bulk buying gives you a bit of leverage;);)
 
Hi, I have a megger 1552 that gives completely different results when
measuring "Hi" & "no trip" impedance values. The Hi value seems to give the most accurate result (compared to another meter) while the no trip value always seems to be a lot higher. It seems to only happen when
trying to test at a particular premises containing 21 flats with 3 phase
incomming supply. Ze (hi) = 0.25 whilst Ze (no trip) = 2.85.
I have had the unit checked by a calibration lab but they cannot find any
faults with the meter. Could this be caused by high voltage fluctuations/ noise in the circuits?
Thanks Wayne
 
You will find that any test meter that has a no trip function will give different readings due to the nature of how it carries out the test without tripping.
 
check for the dvd that came with the tester, its with the calibration cert in the top of the megger box. Shows how to do all the tests. very helpful.

If your doing a zs test why not use the plug attachment that comes with the tester rather than the leads if its a radial socket circuit hth cheers
 
Last edited by a moderator:
I've only ever used the Hi setting and 2 leads for the measurement of Ze. Is this wrong?

Have a look at the following links for some instruction


[ame]http://www.youtube.com/watch?v=PniIhehMNf8[/ame]


[ame]http://www.youtube.com/watch?v=p_Blib9qUO0[/ame]
 
Last edited:
with the 1552 on no trip Zs test you must use 3 leads or the plug-top lead
 

Reply to megger 1552 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

  • Article
Electrical2Go - Megger MFT Deals! Upgrade your toolkit with our exclusive offer! Purchase any of the Megger advanced multifunction testers –...
Replies
0
Views
577
Hi I've got a megger mft 1720 that I was hoping any one can shed any light on When performing continuity tests (even when nulling the leads)...
Replies
13
Views
2K
Hi! Some help would be appreciated! I've just moved into new house, wanting to check insulation resestance etc as getting some nuisance...
Replies
2
Views
306
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Just thinking about selling MFT's and single test equipment. The idea being I buy stuff from Ebay and sell it on ebay, which I am doing at the...
Replies
0
Views
273

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock