Discuss Megger kept tripping RCBO in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
92
hello guys
My megger kept tripping out a Wylex 10a RCBO today, the circuit i just installed and polarity had been checked at evey point i don't understand what the problem could be? I obviously set the meter to no trip
 
i assume you were diong loop tests. did you connect all 3 leads in the right order.?


I'm playing all the right notes, but not necessarily in the right order. Eric Morecambe
 
if doing the test with loads connected, could be that there is some leakage on the circuit and the 15mA that the megger puts into the test takes it over the RCBO's threshold.
 
I've had bother with wylex rcbos tripping on loop tests before, I remember now the only way it stayed on for the test to work was to remove all load from the circuit. I've carried out loop tests before on other makes of rcbos with load on and they don't trip.
 

Reply to Megger kept tripping RCBO in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi! Some help would be appreciated! I've just moved into new house, wanting to check insulation resestance etc as getting some nuisance...
Replies
2
Views
293
Hi all, Wondering if you could offer some advice please. I carried out a small outdoor lighting project today at a commercial property. 4 lights...
Replies
5
Views
852
Hi, Just been scratching my head about this one and wonder if I've missed anything. A few weeks ago I installed a new circuit for a 3kw oven and...
Replies
6
Views
738
Hi Guys, Had a call out today about an odd issue with a newish Creda DT storage heater. Basically.. Storage heaters were installed in one flat...
Replies
4
Views
741
Hi all I don't appear to be able to post in the DIY forum so apologies if this is the wrong place. I live in a block of flats with an external...
Replies
3
Views
782

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock