I have mft1720 with megger fused leads protected by 50mA fused.

On Zdb (not main but garage unit) I wanted to do a Z measurement, set it to high current mode (L-L/L-N and Z) when I attempted to take a reading between live wires it blew the fuse in the Netural wire? I believe you must use high current mode for doing Ze or Zdb, so why should the fuse blow?

cheers

krish
 
not sure exactly how you were doing the test, but sounds like you got something wrong.
 
GS38 compliant probes use 500mA fuses and have an appreciable resistance making them unsuitable when loop testing on live systems.

The fused lead itself will add a small variability into the test result.

Test leads fused at 10A will provide protection from short circuit faults but will not fail under normal testing conditions.

500mA Fused test leads (GS 38) order code 6220-789

10 A Fused leads order code 6220-827
 
Trypod, thanks man for this, I thought it might be something like this, so I will have to order the 10A fused leads, just wandoering if I could cheat and stick a 10A fuse in the GS38 leads I used?

krish




GS38 compliant probes use 500mA fuses and have an appreciable resistance making them unsuitable when loop testing on live systems.

The fused lead itself will add a small variability into the test result.

Test leads fused at 10A will provide protection from short circuit faults but will not fail under normal testing conditions.

500mA Fused test leads (GS 38) order code 6220-789

10 A Fused leads order code 6220-827
 

Reply to Megger MFT1720 loop impedenace test issue in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi I've got a megger mft 1720 that I was hoping any one can shed any light on When performing continuity tests (even when nulling the leads)...
Replies
13
Views
2K
  • Article
Electrical2Go - Megger MFT Deals! Upgrade your toolkit with our exclusive offer! Purchase any of the Megger advanced multifunction testers –...
Replies
0
Views
580
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Looking to replace my current generic test leads that are starting to show signs of variable readings. I also find the crocodile clips don't tend...
Replies
9
Views
5K
Hi, I have a Megger mft1720 and the low current loop test isn’t working properly. Just wondering if anyone else has had issues? Readings are...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock