Discuss Memera 2000 fuse box in the DIY Electrical Advice area at ElectriciansForums.net

S

Stuent

Hi my house has a memera 2000 fuse box. The kind which still requires fuses to be placed in it. Recently it has been tripping on a regular basis every couple of weeks or so.

I have managed to isolate the problem by pulling out one of the 30 amp fuses. This allows all other electric to be on, as soon as I plug this fuse in the unit trips again.

this fuse powers a certain ring on wall sockets the ground floor, on pervious occasions leaving it a few hours seems to resolve the problem.

any ideas why this could be happening. To a layman it would seem to me that the ring is overheating, can this even happen?

I have tried different fuses and it still trips so I know it's not a fuse problem....

help!!!!!
 
Hi, you have done the first part of the investigation a spark would do but to do the next stage you will need a tester costing about £350 upwards and the knowledge/experience to use it.

Your best course of action is to locate a local competent spark and get them to do some tests..

Hope this helps
 
i'm in cheshire. be happy to have a look at it for you.
 
Tel is a great guy with many decades of experience, you can't go far wrong by calling him in.
 
not that many decades. makes me seem old.. oh, i am old. :rofl:
 
have to be sherlock holmes as well. the case of the disappearing OP.
 

Reply to Memera 2000 fuse box in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Our home is about 40 years old and equipped with original two Federal Pacific breaker boxes. Until now we have never had any problems. A 30 AMP...
Replies
0
Views
381
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K
Hi My main feed comes into the garage, feeds into the meter and then out to another box with a 60AMP fuse then into the house...
Replies
20
Views
3K
Does anyone know if the Memera 2000AD fuse box is now obsolete . MY EICR report says there is no RCD protection to 3 circuits so I need to...
Replies
20
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock