Discuss Merlin Gerin 30ma 2 pole RCD MULTI 9 Range, TRIPS (oversensitive?) in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

A

Andyrc

:cool:Hello People, Im completing a "SMALL" Commercial Job, and The SUB main is Controlled by a Merlin Gerin 100amp/30ma RCCB, Single phase,2 pole ( DB is 6 WAY) The New Install is on a TT, as it's out of the Equalpotential Zone, When performing tests, the 30ma RCD(main switch) at the sub main Trips! and not the "local" RCD in the new SPLIT load board, So I am thinking? change, the MAIN supply RCCB for a 100amp/100ma , and then change the MCB's at the the same Board, for 30ma RCBO's where Needed! as some supply "local" sockets in the same Building! ............The other thing is, Now that MERLIN is now SCHNEIDER Electrical,of course just a Diff name, wether a MK 6004s RCCB would be Compatible (costs etc) as looking on line, they look the SAME, .......(SO a 6way DB 100amp/100ma RCD Mainswitch, supplys all the other DB,s Variuos out buildings etc, and my SPLIT Load TT board is supplied from that) also as I live in Cornwall it's a you know what to get hold of things, Cheers People, Andy
 
Last edited by a moderator:
Think you've answered your own question...a 30ma RCd mainswitch will always be problematical....your solution sounds good,but the 100ma will need to be time delayed or it will still trip on a 5x test.
 
RCCB 100AMP/100MA "S" TYPE ARRIVED, from YORK all the way down to Cambourne, Cornwall, over nighter, as EDDY'S had NOTHING between here and there, COST £147!!!!!!!!! over 350 miles! CRAZY!!!!!
 

Reply to Merlin Gerin 30ma 2 pole RCD MULTI 9 Range, TRIPS (oversensitive?) in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Keeping this brief.....................New dwelling.....TT system with 100mA S type rcd protected supply to local board with 30mA RCD. Freelance...
Replies
21
Views
3K
Hello all I have recently installed a sub main in 4mm 3-core SWA, approx length 45 metres, to feed a small garden office. Final circuits in the...
Replies
7
Views
2K
Hi all,looking for some pointers to an RCD problem, I work entirely on large poultry farms, I've only been in post a year, at some point before I...
Replies
6
Views
2K
  • Locked
Hi all I am in an industrial unit and the 100mA RCCB keeps tripping. They use it as the main switch inside of the unit's distribution board. The...
Replies
41
Views
6K
Hi guys I was recently ask by a customer if/how his house could be supplied by his electric car. He wants to charge the car at night on low rate...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock