Posting a message to the forum will remove the above advertisement
  1. angel While you're here, would you mind checking out our Electrician's Insurance section to see if we could save you a few quid? - Specifically our Van Insurance Deals and Public Liability Insurance Deals. Thanks for supporting the forum! angel

    5% Discount from Electrical2Go.co.uk for ALL members! - Click Here

Discuss Metal cable tie distance in the Commercial Electrical Talk area at ElectrciansForums.co.uk.

Please make sure you checkout our forum sponsors, many do discounts for members and, they keep the forum free to use.
  1. Daniel Mills
    Offline

    Daniel Mills New EF Member

    Location:
    Bromley
    I’m working on a commercial construction site and I’ve been requested by he client to install metal cable ties to all inverted tray runs for my beldon and SWA cables.

    I’ve looked through BS7671 and I can’t seem to find the distance required between each metal cable tie.

    Does anyone know where I can find this distance and what distance it is?

    Additionally PVC cable ties are installed, this is just incase of a fire.
     
  2. buzzlightyear
    Offline

    buzzlightyear still kicking sand, before pushing up daisies . Electrician's Arms

    Location:
    star command
    personally I would space them out for cable trays 10inches apart approx.
     
    • Agree Agree x 2
    • Like Like x 1
  3. Andy78
    Online

    Andy78 Trusted Advisor

    Location:
    Kingston upon Hull
    I think the OSG has tables for maximum distances for cable support if you need them, but what Buzz suggested seems right.
     
    • Like Like x 1
  4. Wilko
    Offline

    Wilko Electrician's Arms

    Location:
    Berkshire
    Business Name:
    Wilko Electrics
    OSG Appendix D Table D1 has the spacings :)
     
    • Winner Winner x 1
  5. Murdoch
    Offline

    Murdoch Electrician's Arms

    Location:
    Woking
    Where is it in the BYB?
     
  6. Andy78
    Online

    Andy78 Trusted Advisor

    Location:
    Kingston upon Hull
    I think the regs say something vague and all encompassing like "cables must be adequately supported" then the OSG expands on this with distances for sizes of cables.
     
    • Agree Agree x 1
  7. Wilko
    Offline

    Wilko Electrician's Arms

    Location:
    Berkshire
    Business Name:
    Wilko Electrics
    The next question is - do all of the supports need to be metal to comply with 521.11.201 ?
    I haven't read advice on that, but I've seen some where every clip is metal, some every second clip and some looking retro fitted at 1m.
     
    Last edited: Oct 11, 2017
  8. Richard Burns
    Offline

    Richard Burns Trusted Advisor

    Location:
    Cambridgeshire
    Business Name:
    Richard Burns
    I think I would concur with wilko that the general approach is that there must be some metallic or fire resisting clips at 1m intervals, the remaining supports can be plastic or such like.
    The regulation is as usual for BS7671 fairly vague on wording as Andy78 says it cannot be the sole means of support and must be adequate??
    The intent of the regulation is to prevent cables dropping in a fire and causing a restriction to someone trying to traverse the route.
    Therefore on a high ceiling above 3m a cable that drops one meter down will not impede the majority of people. If the ceiling is low then a smaller drop could be a problem, so a risk assessment of the amount that cables could drop would be a good idea to ascertain the frequency of fixing.
    Having said that if the cable is metallically intact then it should not drop far even if the insulation and sheathing are gone so long as there are regular intact supports.
     
    • Like Like x 3
  9. Murdoch
    Offline

    Murdoch Electrician's Arms

    Location:
    Woking
    Which is just madness. That table should be in theBYB....
     
  10. Andy78
    Online

    Andy78 Trusted Advisor

    Location:
    Kingston upon Hull
    The way the regulations are worded for cable supports allows for experience and good workmanship to figure out what is adequate. The OSG takes the "dummies guide" approach though I suppose.

    The regs are 522.8.4 and 522.8.5
     
  11. stevethesparks
    Offline

    stevethesparks Electrician's Arms

    Location:
    Northampton
    But if common sense were applied, there would be no need to sell both books to us mugs.
     
    • Like Like x 1
    • Agree Agree x 1
  12. Risteard
    Offline

    Risteard Electrician's Arms

    Location:
    Derry, Ireland
    Business Name:
    Walsh Electrical Services
    SWAs secured with cable ties is not great to be honest (although fairly common). They should really be cleated to the tray.
     
    • Agree Agree x 1
Loading...
Similar Threads - Metal cable distance Forum Date
Metal clips............... Electrical Tools and Products Jul 5, 2018
PME METAL OUTBUILDING Electrical Forum Jul 3, 2018

Share This Page

Users found this page by searching for:

  1. fire alarm cable tie distance

    ,
  2. spacing between cable ties on cable tray

    ,
  3. fire alarm cable tie regs

Electricians Directory Post a Domestic Job Post a Commercial Job