ab6014

-
Reaction score
0
The background: I'm building a rig for an engineering project to age polymers, using UV radiation and water cycles. The power supply, water pump and actuator (use not relevant) are controlled via an Arduino.
The rig has worked in the past with Infrared bulbs (for a different project). I'm now switching to UV bulbs which require ballast and ignitor to run.

The problem: I wired up one bulb to begin with, the bulb turned on but after I turned the circuit off, the power tripped (large circuit breaker for the entire run of sockets in the laboratory).
Second attempt, checked the wiring and wired up both lamps in series. This time the bulbs did not turn on, but the power tripped again.

Ballast Link: https://uk.rs-online.com/web/p/lighting-ballasts/7840515/
Ignitor Link: https://uk.rs-online.com/web/p/lighting-ignitors/6677268/
UV Bulb Link: https://uk.rs-online.com/web/p/uv-curing-lamps/8298870/
Circuit diagrams for series and single bulbs respectively:
circuit-diagrams-jpg.143021


The only issue I can think of causing the trip is that I'm yet to properly earth the circuit. Similarly for the two bulbs not operating at all, I'd guess it was a more fundamental issue with running the lamps in parallel as shown, I've not seen a diagram online like this, I simply assumed it would be okay.

Thanks in advance, Adam
 
The background: I'm building a rig for an engineering project to age polymers, using UV radiation and water cycles. The power supply, water pump and actuator (use not relevant) are controlled via an Arduino.
The rig has worked in the past with Infrared bulbs (for a different project). I'm now switching to UV bulbs which require ballast and ignitor to run.

The problem: I wired up one bulb to begin with, the bulb turned on but after I turned the circuit off, the power tripped (large circuit breaker for the entire run of sockets in the laboratory).
Second attempt, checked the wiring and wired up both lamps in series. This time the bulbs did not turn on, but the power tripped again.

Ballast Link: https://uk.rs-online.com/web/p/lighting-ballasts/7840515/
Ignitor Link: https://uk.rs-online.com/web/p/lighting-ignitors/6677268/
UV Bulb Link: https://uk.rs-online.com/web/p/uv-curing-lamps/8298870/
Circuit diagrams for series and single bulbs respectively:
circuit-diagrams-jpg.143021


The only issue I can think of causing the trip is that I'm yet to properly earth the circuit. Similarly for the two bulbs not operating at all, I'd guess it was a more fundamental issue with running the lamps in parallel as shown, I've not seen a diagram online like this, I simply assumed it would be okay.

Thanks in advance, Adam
What is tripping CB or RCD?
 
The background: I'm building a rig for an engineering project to age polymers, using UV radiation and water cycles. The power supply, water pump and actuator (use not relevant) are controlled via an Arduino.
The rig has worked in the past with Infrared bulbs (for a different project). I'm now switching to UV bulbs which require ballast and ignitor to run.

The problem: I wired up one bulb to begin with, the bulb turned on but after I turned the circuit off, the power tripped (large circuit breaker for the entire run of sockets in the laboratory).
Second attempt, checked the wiring and wired up both lamps in series. This time the bulbs did not turn on, but the power tripped again.

Ballast Link: https://uk.rs-online.com/web/p/lighting-ballasts/7840515/
Ignitor Link: https://uk.rs-online.com/web/p/lighting-ignitors/6677268/
UV Bulb Link: https://uk.rs-online.com/web/p/uv-curing-lamps/8298870/
Circuit diagrams for series and single bulbs respectively:
circuit-diagrams-jpg.143021


The only issue I can think of causing the trip is that I'm yet to properly earth the circuit. Similarly for the two bulbs not operating at all, I'd guess it was a more fundamental issue with running the lamps in parallel as shown, I've not seen a diagram online like this, I simply assumed it would be okay.

Thanks in advance, Adam
What is tripping CB or RCD? Bit silly not earthing your rig
 
Unfortunately I cant tell, its all locked away and needs to be reset by a technician which takes a few hours, so I cant use it to troubleshoot.
I was getting round to the earthing!, was only provisionally testing it to begin with.
Since posting, I've decided to include the capacitor shown below. https://i.stack.Upload the image directly to the thread.com/4n8i7.gif
But i'm unsure what size it should be and still not sure why the series arrangement didn't work at all.
 
So I've solved the tripping issue with the added capacitor as shown in the previous diagram.
Now that it is all fine with one bulb, any ideas on why it would not start with the 2 bulbs in parallel as per the first image?
 
tripping probably caused by inrush current, no reason why they should not operate in parallel. in series they won't work as each only gets 120V. maybe a c or d type breaker will cure the tripping, Zs permitting.
 

Reply to Metal Halide Circuit Issues in the Lighting Forum area at ElectriciansForums.net

Similar Threads

Hi all, I've been having some issues trying to fix a fluorescent light in the bathroom. Here's the steps I've taken so far after it suddenly...
Replies
8
Views
1K
Hello all, Ran into a curious issue last night with my basement light circuit - here are the details of the circuit (diagram also attached): 15a...
Replies
0
Views
1K
Having lost my father in law many years ago, an electrician and electrical engineer, I'm now at a loss for a sounding board for any issue that...
Replies
1
Views
1K
Hi All. New member. I have a perplexing issue which I am hoping someone might be able to help with. I have two suspension lights which are...
Replies
10
Views
3K
Hi I have bought a small fan and it is a 12v dc It has a thin red and black wire attached. I was wondering if anyone would be kind enough to...
Replies
14
Views
2K
Squid
S

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock