Discuss Meter Tails - Neutral in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Yeah I know was wondering the works the OP was carrying out. I believe in the 16th Ed this type of cable was acceptable for containment in walls without additional protection, come the 17th or maybe a 16th Amm, can't remember it disappeared. So whether by intention or not at the time of installation it would have complied.
 
Because it is from an 80A supply at dno fuse and offers no protection. Is unlikely to be 50mm deep anywhere
If it is 16.0 then clipped direct or buried in ground it will take 80A, your cable however may need correction factors applied to it and without information from the manufacturer you are not going to know.
Is the cable relying on the service head fuse, if so how long is the run and how do you know it is 80A.
 

Reply to Meter Tails - Neutral in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all, Customer has an extension and this compromises existing meter position, DNO is extending incomer and putting meter box on a different...
Replies
3
Views
360
Hi, Ignoring the appauling conductor terminations which I found, in the background of the photo you can see a really odd neutral tail terminated...
Replies
17
Views
2K
Just wanted to know which people use. My case. Client converting attached garage into new rooms. Consumer Unit has to move to accomodate this...
Replies
7
Views
1K
I didn't get a picture so will have to wait until I go back again but I've done a crude drawing of what was there. Its in a commercial set up...
Replies
13
Views
2K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock