Discuss Missing cpc in domestic lighting circuit in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

codger

-
Reaction score
12
Morning. A friend and I have been carrying out some EICRs on properties in our area. Recently, my mate has come across two houses in which the lighting circuits do not have any earthing at all. They have been run in twin and earth but the earths have all been snipped off at lighting points, switches, jointboxes etc. The colours of the cable are black and red (give you an idea of the age of the installation). The ceiling, floors and walls are all concrete and it looks like the twin and earths have been dropped down conduit drops to the switches.

As far as the EICR goes what would you put this down as...? We're thinking C2. Someone else suggested that it goes down as a C3 as long as it's stipulated that only plastic fittings should be used.

Cheers
 
The cpcs should be terminated but the Coding would depend upon if any back boxes, accessories or fittings need the connection of a cpc for fault protection. Are they metal back boxes and if so do they incorporate nylon fixing lugs because they don't need earthing. If they have cut them out sounds like a rough job.
 
The cpcs should be terminated but the Coding would depend upon if any back boxes, accessories or fittings need the connection of a cpc for fault protection. Are they metal back boxes and if so do they incorporate nylon fixing lugs because they don't need earthing. If they have cut them out sounds like a rough job.

They are metal boxes....no plastic inserts though. I know the ones you mean. We've peered up at a switch and spotted that it looks like the old conduit system....the ones where the switch back boxes had a wee spigot that pushed onto the end of the conduit drop.
 

Reply to Missing cpc in domestic lighting circuit in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Have been asked to do remedials on an EICR that was carried out a year or so ago by another electrician. Curious to know what code you would give...
Replies
12
Views
1K
I'm getting an old fuse board upgraded in an office block. The electrician has just told me that most of the circuits don't have earth cables...
Replies
44
Views
3K
Old two core cable in a lighting circuit with no cpc at any point All points had metal fixtures and fittings class1 At two points the live loop...
Replies
0
Views
599
I've tried to research and form a plan without asking on here, but I'm just going around in circles. Just completed an EICR. The wiring ranges...
Replies
15
Views
2K
Strange on this, we are wiring an extension at the moment and I would like to 3 way the (currently 2 way) landing switch to the new bedroom so...
Replies
14
Views
553

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock