Hello,

I am replacing a consumer unit in a house which has been divided into flats.

It is a TT system and has a 100ma rcd main switch before the distribution board which feeds the 3 flats each protected by a 40a 30ma rcbo. (located ground floor hallway)

does the consumer unit in each flat need another set of 30ma rcds to protect each circuit or would normal mcbs be sufficient as the board is already fed from 40a 30mA rcbo!

am i right in thinking theres no way of setting up any discrimination anyway?

Thanks
 
It would be far better if the existing main switch was replaced for a 100ma time delayed type ,and the rcbo's were replaced for mcb's, and each flat was provided with rcbo's for final circuits...that way a fault in a flat wouldnt neccessitate a trip to the intake to reset.....As it stands if you are just relacing the cu in the flat there is no point in providing additional RCD's as the RCBO at the intake cover the whole flat...not very satisfactory though.
40A??.....hope they are not planning on having a 9kw shower and a new range in the kitchen:eek:
 
ah thanks for your advice, yea think as you say mcbs at the intake and rcbo's for the final circuits would be a much better set-up! i'l have to check what i've got to work with and come to a decision! thanks again
 

Reply to more than 1 rcd? in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock