eyeball

Hi Guys,
I went to see a job the other day and even though its a new splitload C/U, it had about 3 breakers with more than one circuit wired in. ie ....

6A Breaker feeding a1.5mm radial for the main lights and a 1.5mm radial for the house alarm

20A Breaker with 2.5mm radial feeding one single double socket in the loft and a 2.5mm radial feeding one single socket in a bedroom.

32A Breaker with a 4.0mm radial feeding the washing machine and a fridge and a 4.0mm radial feeding a seperate C/U int the conservatory and this was split for 2 strip lights and for the use of a freezer.

Now what would you do in my posistion regarding this situation as the location of the C/U is very tight and wouldnt stretch to a larger unit with more ways?

Finally the Shower was a 9.5 KW fed with 6mm clipped direct and only about a 6m length, this was protected by a 40A. I measured the Amp draw whilst it was on full power and lest it on for quite some time and it never got near 30Amps never mind 40...marginal cable but the sums seem to add up...should I change the cable???:confused:
Cheers...
 
Hi Guys,
I went to see a job the other day and even though its a new splitload C/U, it had about 3 breakers with more than one circuit wired in. ie ....

6A Breaker feeding a1.5mm radial for the main lights and a 1.5mm radial for the house alarm No problem

20A Breaker with 2.5mm radial feeding one single double socket in the loft and a 2.5mm radial feeding one single socket in a bedroom. Again,no problem

32A Breaker with a 4.0mm radial feeding the washing machine and a fridge and a 4.0mm radial feeding a seperate C/U int the conservatory and this was split for 2 strip lights and for the use of a freezer. Would be preferable to split...but complies with regs

Now what would you do in my posistion regarding this situation as the location of the C/U is very tight and wouldnt stretch to a larger unit with more ways?

Finally the Shower was a 9.5 KW fed with 6mm clipped direct and only about a 6m length, this was protected by a 40A. I measured the Amp draw whilst it was on full power and lest it on for quite some time and it never got near 30Amps never mind 40...marginal cable but the sums seem to add up...should I change the cable???:confused:
Cheers...
A 9.5kw load should pull over 41a...exceeding the rating of the MCB but not the cable @ 47 amps clipped direct...at 6m volt drop is <2V.....as long as the mcb is not tripping during use I wouldnt worry about it.
 
in regards to the circuits mate, the 6a supply to the burglar alarm is allowed as its a spur off the circuit, as is the radial sockets. as for the shower, i make it 41A assuming 230v and a power factor of 1.
 

Reply to More than one ciruit in a breaker? in the Australia area at ElectriciansForums.net

Similar Threads

  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hi all, I’m new to this forum so please bear with me. I live in a bungalow and would like to repurpose an unused shower cable to supply one new...
Replies
0
Views
4K
Ok guys been asked help mate out but i think he has done his install wrong but as misplace my regs book cant find exact regulations he...
Replies
21
Views
8K
Hi guys, I'm about to fit a new kitchen and I have ordered two single ovens which are Bosch. They are rated at 2.99KW. They are both going in a...
Replies
16
Views
16K
Morning - just a photo for info to show what's out there (as if most don't already know!!!) & to reiterate the ignorance of some householders. A...
Replies
32
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock