eyeball
Hi Guys,
I went to see a job the other day and even though its a new splitload C/U, it had about 3 breakers with more than one circuit wired in. ie ....
6A Breaker feeding a1.5mm radial for the main lights and a 1.5mm radial for the house alarm
20A Breaker with 2.5mm radial feeding one single double socket in the loft and a 2.5mm radial feeding one single socket in a bedroom.
32A Breaker with a 4.0mm radial feeding the washing machine and a fridge and a 4.0mm radial feeding a seperate C/U int the conservatory and this was split for 2 strip lights and for the use of a freezer.
Now what would you do in my posistion regarding this situation as the location of the C/U is very tight and wouldnt stretch to a larger unit with more ways?
Finally the Shower was a 9.5 KW fed with 6mm clipped direct and only about a 6m length, this was protected by a 40A. I measured the Amp draw whilst it was on full power and lest it on for quite some time and it never got near 30Amps never mind 40...marginal cable but the sums seem to add up...should I change the cable???
Cheers...
I went to see a job the other day and even though its a new splitload C/U, it had about 3 breakers with more than one circuit wired in. ie ....
6A Breaker feeding a1.5mm radial for the main lights and a 1.5mm radial for the house alarm
20A Breaker with 2.5mm radial feeding one single double socket in the loft and a 2.5mm radial feeding one single socket in a bedroom.
32A Breaker with a 4.0mm radial feeding the washing machine and a fridge and a 4.0mm radial feeding a seperate C/U int the conservatory and this was split for 2 strip lights and for the use of a freezer.
Now what would you do in my posistion regarding this situation as the location of the C/U is very tight and wouldnt stretch to a larger unit with more ways?
Finally the Shower was a 9.5 KW fed with 6mm clipped direct and only about a 6m length, this was protected by a 40A. I measured the Amp draw whilst it was on full power and lest it on for quite some time and it never got near 30Amps never mind 40...marginal cable but the sums seem to add up...should I change the cable???
Cheers...