Discuss Moving to radials in Kitchens in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
31
I'm going to quote for a kitchen rewire shortly where the client is having a new kitchen fitted and new appliances and am contemplating doing away with the traditional 2.5 ring final on a 32amp mcb and running a 4mm radial instead. Clipped direct is 36amp so could still use a 32amp but with todays energy efficiency could probably even use a 20amp mcb and have the option to move up to 32 if needed.

Just wanted to see what peoples thoughts are whether anyone has done it or if the ring final in the kitchen is here to stay?
 
At the risk of sounding completely noob... I didn't even realise they did 25amp hahaha! Even better can't see newer appliances using close to that these days so that will be fine and plenty under the max carrying capacity, thanks mhar
 
At the risk of sounding completely noob... I didn't even realise they did 25amp hahaha! Even better can't see newer appliances using close to that these days so that will be fine and plenty under the max carrying capacity, thanks mhar
not all manufacturers do 25A MCBs and even those that do, rare to find them in wholesaler's off the shelf.
 
I'm going to quote for a kitchen rewire shortly where the client is having a new kitchen fitted and new appliances and am contemplating doing away with the traditional 2.5 ring final on a 32amp mcb and running a 4mm radial instead. Clipped direct is 36amp so could still use a 32amp but with todays energy efficiency could probably even use a 20amp mcb and have the option to move up to 32 if needed.

Just wanted to see what peoples thoughts are whether anyone has done it or if the ring final in the kitchen is here to stay?
Just use a standard 32Amp radial wired in 4mm2 as long as the area isn't greater than 75M2 BS 7671 App 15 can't see where the confusion lies.
 
Just use a standard 32Amp radial wired in 4mm2 as long as the area isn't greater than 75M2 BS 7671 App 15 can't see where the confusion lies.

Doesn't take much of a de rating factor to make 4mm unsuitable for a 32A MCB.

Although the OP will calculate this as part of his design.
 
Have done a few kitchen refurbs using 4mm radials

Especially when the entire house is on 1 ring main I take the entire kitchen off the ring main and just wire it in 1 or 2 new 4mm radials depending on loads etc

I actually quite like doing it this way
 
I often use radials domestic and commercial. There is some advantages to this. Testing is straightforward and installation in many ways. I usually do 32a. While I agree that wont work for some situations regarding C factors most of the time it does and more so for commercial. While you can do branching with radial circuits, much like the continental method I think it can become a nightmare later when additions and alterations come in to it. As well it is difficult to put three 4mm² into the terminations on sockets. It is a matter of judgement of course regards use of and future use as to whether a radial will be suitable load wise. Never had any problems so far with overloads.
 
At the risk of sounding completely noob... I didn't even realise they did 25amp hahaha! Even better can't see newer appliances using close to that these days so that will be fine and plenty under the max carrying capacity, thanks mhar

You know I was pondering whether this is a misnomer, most kitchen appliances will be no more efficient that in days of yore.

Anything with a heating element will require pretty much the same input to achieve it's purpose.

There are exceptions, obviously:-

Washing machines = wash colder
Fridges/Freezers = Better insulated.
Condenser Dryers

Things that will draw similar current:-

Oven
Hob (dedicated circuit though)
Kettle
Toaster
Blender/Mixer
Microwave
Extractor Hood
Tumble dryers

Then of course there is the multitude of crap that we never used to have.

Dishwasher
Coffee maker
Juicer
Smoothie maker
TVs
Plate warmer
Steam oven
Plinth heater
second ovens
Instant hot water taps


It would be extremely difficult to over load 4mm cable on a domestic kitchen

You ain't seen my missus attempting a Sunday roast.
 
I often use radials domestic and commercial. There is some advantages to this. Testing is straightforward and installation in many ways. I usually do 32a. While I agree that wont work for some situations regarding C factors most of the time it does and more so for commercial. While you can do branching with radial circuits, much like the continental method I think it can become a nightmare later when additions and alterations come in to it. As well it is difficult to put three 4mm² into the terminations on sockets. It is a matter of judgement of course regards use of and future use as to whether a radial will be suitable load wise. Never had any problems so far with overloads.
You can, if you wish wore 1 non fused from a 4mm2 32 Amp radial in 2.5mm2 or if you want a fused spur in 1.5mm2, providing you don't go over 75M2 floor area.
 

Reply to Moving to radials in Kitchens in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Currently planning a new rewire for my kitchen and want to get things right first time when it comes to appliances consumptions and circuits...
Replies
0
Views
930
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
592
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
631
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
779
HI All, I am building a new house (self build) and have my part P so am running the cabling. My reading of the regs says that any appliance of...
Replies
18
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock