    before changing db you have to prove that the installation is ok to accept 17th edition boards a landlord has asked me to change 12 in a block of flats now usually i would do full test on boards but bearing in mind the prices are tight not wanting to spend to much time would i get away with just an insulation test between LN together to earth your thoughts please
     
  2. telectrix
    Offline

    telectrix Scouser and Proud of It Respected Member

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    visual inspection, then IR . test for borrowed neutrals. if you have an earth leakage clamp meter, check if there's any apparent earth leakage. measure Ze. CONFIRM EARTHING AND BONDING. lack of bonding can bite you in the pocket.
     
    Last edited: Feb 24, 2012
  3. Farmelectrics
    Offline

    Farmelectrics Farmelectrics Electrician's Arms

    Location:
    Wirral
    Business Name:
    Farm electrics
    once the new board was fitted a full test will be done and cert issued but is the above test good enough for me to change board done this in past and got readings ranging from 8Mohms upwards
     
  4. tony mc
    Offline

    tony mc Electrician's Arms

    The above tests should be enough to change the board and if the IR tests are 8 Meg and above the RCD's will hold no problem at all.

    Its the unexpected faults that you have to look for ie no continuity on final rings ccts very high R1 +R2 readings on radials which need further investigation etc etc.
     
  5. telectrix
    Offline

    telectrix Scouser and Proud of It Respected Member

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    if time allows, might be a good idea to take a few Zs readings and end/end continuity of RFC/S.
     
    • Like Like x 1
Loading...
Similar Threads - multi consumer board Forum Date
Multicore cable voltages Electrical Wiring, Theories and Regulations Wednesday at 1:54 AM
2+2=4? Multiple 2A plug puzzle Electrical Forum Saturday at 2:27 PM
Thread Status:
Not open for further replies.

Share This Page

Electricians Directory Post a Domestic Job Post a Commercial Job