  1. tank
    Offline

    tank Regular EF Member

    Doing an eicr on a landlord board, in a small 1940s block of bedsits, found a type 2, 30amp socket ring breaker with 5 x 2.5mm cables in it. I assume that 2 of the wires came from an empty adjacent 30 amp heater ring breaker that had been damaged (screwdriver busbar metal board bang) and the 5th wire, a spur maybe, or something else.

    I just wanted to know how other people would approach this situation.

    I looked, concluded that the conductors were inadequately identified for any tests to proceed, wrote FI the cert, and moved on. Any thoughts?
     
  2. Murdoch
    Offline

    Murdoch Electrician's Arms

    Location:
    Woking
    if you are "doing" an EICR you first need to establish what all the circuits are connected to (I suspect most cheap EICR's don't do this) - in this situation determining which 2 are the ring should be easy ..... but I suspect if you haven't allowed enough time then you need to C2 / FI said circuit.

    As for stopping the inspection ..................... I disagree.
     
    • Like Like x 4
    • Agree Agree x 1
  3. Dannyg8810
    Offline

    Dannyg8810 Electrician's Arms

    Location:
    Leeds
    If any of the cables are not under rated for the protective device can't see a problem
    But suppose you'd need to trace it all back to see all is ok
     
  4. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Staff Member Moderator

    Location:
    Northamptonshire
    You are doing an EICR crack on and test it don't find an excuse not to. Just having five 2.5s on an mcb is an issue in itself but from your terminology I must question whether you are up to the task.
     
    • Dislike Dislike x 2
    • Agree Agree x 1
  5. Murdoch
    Offline

    Murdoch Electrician's Arms

    Location:
    Woking
    Not sure I agree with that.

    Our last house had a similar set up prior to a CU change from a 3036 board - 2 x rings + 1 x spur at CU. Very unlikely to overload - but when I changed the CU, I separated the 2 rings.
     
    • Agree Agree x 1
  6. tank
    Offline

    tank Regular EF Member

    Yes, the amount of time I was allocated for the job certainly influenced my decision. To clarify, it was on to the next circuit that I moved after the FI.
     
  7. Murdoch
    Offline

    Murdoch Electrician's Arms

    Location:
    Woking
    Out of interest, how big was the property and how long were you allocated?
     
  8. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Staff Member Moderator

    Location:
    Northamptonshire
    Nothing to do with overcurrent but the connection of five conductors.
     
  9. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Staff Member Moderator

    Location:
    Northamptonshire
    So a charge has been made for an EICR but any circuit which appears to be tricky, FI and job done.
     
    • Like Like x 3
  10. Flanders
    Offline

    Flanders Regular EF Member

    Location:
    Tamworth
    In this situation although it is technically one circiut i would break it down to the seperate circuits they effectively are and write them out on the report, if they are connected to way 1 i would write for example
    1a sockets up.....
    1b sockets down..
    1c heater ......
    I would say it not further investigation unless its not clear what ths circuits do
     
    • Like Like x 2
  11. Murdoch
    Offline

    Murdoch Electrician's Arms

    Location:
    Woking
    was fine in my old Wylex board - a far superior connection with 2 screws than the carp we install these days ......
     
  12. polo1
    Offline

    polo1 Electrician's Arms

    Location:
    Glasgow
    Business Name:
    GW Electrical & Security
    5 x 2.5mm conductors in a single Wylex fuse connection, Murdoch. Really?
     
  13. Des 56
    Offline

    Des 56 Forum Mentor

    Location:
    Gliese 581C
    The thread title saying multiple circuits in the mcb is in itself contentious
    However many conductors it is one circuit

    Having said that,lets be realistic,five conductors in one mcb is stretching the point
    At the minimum its a alteration to an existing which has probably made the installation standard lower

    I don't like the idea of further investigation and never have
    For whatever reason FI is a cop out,either by the tester,the company that employs him or the shallow pockets of the client who's concern for safety could not be the main reason for the eicr
     
    • Like Like x 1
Loading...
Similar Threads - Multiple circuits breaker Forum Date
Earth fault loop impedance, initial verification, multiple DB Electrical Wiring, Theories and Regulations Nov 7, 2018
Multiple TT outbuildings Electrical Wiring, Theories and Regulations Oct 17, 2018
Thread Status:
Not open for further replies.

Share This Page

Electricians Directory Post a Domestic Job Post a Commercial Job