    I have a DC 24v Fan, which at full load uses around 7Amps.

    I brought a DC 24v 13A PSU Driver, which when i first tested the fan powered it just fine.

    After a week or so went by, I reconnected the driver again, and now the fan doesnt spin even 2% of what it did before.

    The fan just about rotates(not very fast spin at all) for half a second then stops for 5 seconds then makes a weak half a second rotation again.

    Around 2 seconds after I unplug the PSU Driver or dissconnect it from the fan, the fan spits out one last weak rotation attempt for a bit longer than half a second.

    Is the fan at fault or the PSU?
     
  2. Marvo
    Offline

    Marvo Admin and gender confused Staff Member

    Location:
    South Africa
    Was the driver/PSU sold as a unit together with the fan of did you purchase them separately? If it was sold as a 'driver' it might be a constant current supply rather than a constant voltage type.

    Do you have a tester? Connect the fan to the power supply and test the voltage under load on the DCV scale.
     
    • Agree Agree x 1
  3. JackBoy
    Offline

    JackBoy EF Member

    Location:
    london
  4. Pete999
    Online

    Pete999 Trusted Advisor

    Top Poster Of Month

    Location:
    Northampton
    Business Name:
    None
    " they was not sold together" sorry mate you're from London should have realised:cool:;):rolleyes:
     
  5. Richard Burns
    Offline

    Richard Burns Trusted Advisor

    Location:
    Cambridgeshire
    Business Name:
    Richard Burns
    I would suspect that a component in the driver is overheating and cutting out.
    The power supply should be a constant voltage unit and should be able to power the fan without problem so I'd be asking for a refund or replacement from the PSU supplier.
    However if you have a couple of 12V batteries it would be worth just connecting the fan to them in series to check the fan works and measure the current drawn.
     
    • Agree Agree x 1
  6. Marvo
    Offline

    Marvo Admin and gender confused Staff Member

    Location:
    South Africa
    I can't find any datasheet for the particular item you linked to on EBay but it looks to me like a unashamed direct rip-off of the MeanWell 350W constant voltage switchmode driver which I've used a lot in the past.

    Regardless, the supply should give a 24VDC output under an appropriate load so test the voltage with your fan connected and anything less than 23V and more than 25V send it back for a refund.

    Here's the MeanWell spec sheet but please note I can't guarantee you're unit is the same specs.
     

    Attached Files:

  7. JackBoy
    Offline

    JackBoy EF Member

    Location:
    london
    @Pete999@Pete999 @Richard Burns@Richard Burns

    You lost me Pete999, can you elaborate?

    I purchased another of the PSU, and am having the same issues with it as the first.
    @Marvo@Marvo I tested the voltage without the fan connected, the voltage on the PSU reads 24.0V - on both PSU - which is just perfect.

    When connecting the fan, and then testing the Voltage the reading shows 0.2V, then every 5 seconds or so when the fan kicks, the Voltage jumps to around 1.0V.
    Lastly when unplugging the PSU, the fan has one big last kick after it is unplugged, the voltage of that kick goes up to 2.0V.

    Putting the Voltage test aside, I kept touching the fan wires to the PSU over and over, and maybe one out of 20 times the fan seemed to spin at full 24V and stay on until I removed the wires...
    It seemed that if I left the PSU on for a while w/o any load, and then touched the fan wires on the terminals after 40 seconds, I am more likely to get the fan to spin at 24V correctly. but if I keep touching the fan wire to the terminal it never seems to work...

    What could the voltage test indicate? And what could the scenario I posted below that indicate?

    Fan or PSU?

    Also guys one last question, I attempted to use this PWM 2Pcs PWM DC Motor Speed Control Switch Controller Volt Regulator 12V~40V 10A | eBay - http://www.ebay.co.uk/itm/152558432200
    with the PSU and Fan, is there anyway this could damage the PSU's?
     
  8. JackBoy
    Offline

    JackBoy EF Member

    Location:
    london
    I am also wondering whether to get a higher amperage PSU? 24V 20Amp, currently I have 24V 15A
     
    • Like Like x 1
  9. Richard Burns
    Offline

    Richard Burns Trusted Advisor

    Location:
    Cambridgeshire
    Business Name:
    Richard Burns
    Since you have what is a fairly powerful 200W fan it is possible that the initial start current of the fan may exceed the overcurrent protection of the PSU if this operates instantly and this shuts down the voltage output and then resets after a short time to start to power the fan which then overloads the PSU again, occasionally if you hit the right point in the output or the fan is still turning slightly then it may be able to overcome this and start normally.
    If this is the case, though it is very hard to measure for without an oscilloscope type monitor then a more powerful PSU may be able to cope without exceeding the overcurrent protection. If it is to the same spec as Marvo linked to then it can withstand an overload for 5s which should be in the order of 1000 times as long as required so I am not certain this is the case, but the symptoms point in this direction.
    Possibly applying a NTC resistor to limit the start up current maybe a way of assessing if this is the case and may resolve the situation at a much lower cost.
    The speed controller should have no perceptible back feed effect to the PSU as the input should be filtered and the fan shouldn't worry about the the input supply, it should be controlled readily.
     
    • Like Like x 1
  10. Wilko
    Offline

    Wilko Electrician's Arms

    Location:
    Berkshire
    Business Name:
    Wilko Electrics
    As RB has said, it's possible the supply is shutting down due to startup load. I'd try a series resistance (maybe add in a car stop lamp?) and see if the supply will at least run up to 24V.
     
    • Like Like x 1
  11. JackBoy
    Offline

    JackBoy EF Member

    Location:
    london
    Hi guys, thanks for the replies.

    The problem is I dont have access to these components you are talking about.
    I am going to try buying a larger Amp PSU, do you think a 24v 20A should be ok to deal with the insurge? (my previous one in question was a 24V 15A).

    Or the next sizes up are 24v 25A, 24v 30A...
     
  12. JackBoy
    Offline

    JackBoy EF Member

    Location:
    london
    Also, I phoned the PSU supplier, they said that perhaps the fan is appearing as a dead short to the PSU, and therefore the PSU cuts out when it notices it.

    Could that be possible? wouldnt that make the fan faulty?
     
  13. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
     
  14. JackBoy
    Offline

    JackBoy EF Member

    Location:
    london
    @telectrix@telectrix yep, thats exactly the path any electrical job I attempt ends up going, highway to f**king hell
     
  15. Wilko
    Offline

    Wilko Electrician's Arms

    Location:
    Berkshire
    Business Name:
    Wilko Electrics
    A stationary DC motors appears (to the supply) as the resistance of the windings and so it's normal for the motor to try to draw a high starting current. I think you need to find a way to limit that starting current, as you could double your psu and it might not be enough.
     