Haha I see what you mean mate, it does look a bit like that !:laugh3: Found another of my little jobs from around 3-4 years ago, this was an old house undergoing total refurbishment, unfortunately the idiot builder plastered the wall where the CU is before the cables coming down from above were in place [a load coming up from floor level were in oval conduit due to exposed beams in that room and no wiring allowed 'on show'] but the owner was putting a cupboard there anyway. That was a nice old house to work on, right out in the wilds and most of the time I was there alone, a really tranquil place. :smiley2: View attachment 31019View attachment 31018


as previously asked is this a tt system? Theres no dno earth and you havent got a rcd main switch at origin.?
 
as previously asked is this a tt system? Theres no dno earth and you havent got a rcd main switch at origin.?

What makes you think it's TT? I'm viewing the pic on an iPhone so you may be able to see a bigger pic on another device but I can't see a head in the pic to determine wether it's a DNO supplied earthing arrangement. You can see a 16mm Earth though....even it was a TT system why does it require an RCD as the main switch? It's a dual RCD board...It may be prudent to have an S-type upfront but not an actual requirement. Could you post a few pics of a recently completed CCU you have done?
 
If it is a TT supply, the meter tails are run on the surface & are entering an insulated CU. All the circuits appear to have additional protection via RCD. Why would it need RCD main switch at origin? Take it you mean a S type RCD?

Edit: beaten by Lee
 
If it is a TT supply, the meter tails are run on the surface & are entering an insulated CU. All the circuits appear to have additional protection via RCD. Why would it need RCD main switch at origin? Take it you mean a S type RCD?

Edit: beaten by Lee


well i was always taught and still belive all tt system should have upfront rcd at origin for fault protection, if you are relying on the 30mA rcd in these mass produced dbs then althought ok to cover your own arse at install what happens in the future when these low end rcd's break down and the originalsinstallers poor tt 3/8 rod degrades leaving unacceptavle Ra to operate overload device within disconection times, the install is then in a very unsafe state for the building and user! Why has the op not stated if this is a TT and could shed more light on the install in question
 
years ago, it was common to fit an upfront RCD to a TT system for fault protection where some or most of the circuits were not RCD protected. with the introduction of the 17th ed. now all circuits ( in a domestic property) are generally on RCD since the "buried<50mm deep" reg. came into force. now it's genarally accepted that the CU RCD/s will give that fault protection.
 
So this rcd could be leaving the install in a dangerous state untill the next test, and the next test always gets done on due date lol. I stick to my guns a 100mA type S upfront on a domestic TT at origin is the best way to install that system
 
So this rcd could be leaving the install in a dangerous state untill the next test, and the next test always gets done on due date lol. I stick to my guns a 100mA type S upfront on a domestic TT at origin is the best way to install that system
how? it is relatively easy in a lot of places to get a really low ra so why is an additional rcd needed in all cases
 
nobody's disputing that it's the best way, just not required by regs.
 
So this rcd could be leaving the install in a dangerous state untill the next test, and the next test always gets done on due date lol. I stick to my guns a 100mA type S upfront on a domestic TT at origin is the best way to install that system
Why type s? I thought 100ma would offer enough discrimination from a 30ma? Read somewhere 3 times as much, so for discrimination 90ma or higher should act independently without the need for a time delay
 
So this rcd could be leaving the install in a dangerous state untill the next test, and the next test always gets done on due date lol. I stick to my guns a 100mA type S upfront on a domestic TT at origin is the best way to install that system
As Tel says, believe this was a common design a few years ago and perhaps a few sparks still use it. You may find that difficult with A3? The same could be said of the reliability of MCB's, at least an RCD can be tested. What if the S type goes faulty, how do you design that out
 
Last edited:
Why type s? I thought 100ma would offer enough discrimination from a 30ma? Read somewhere 3 times as much, so for discrimination 90ma or higher should act independently without the need for a time delay
Can't give you the science others will, but time delay rcd is a better design, as I've been advised before.
 
hightower i recommend you have a look on google at discrimination. if you have a 100ma ac rcd and then a 30ma ac rcd they will both trip at once on fault.


an s type or time delayed is recommended because it allows any rcd's/mcbs down stream to clear the fault without tripping.

130-500ms for wylex s type rcd.
 
Last edited:
Why type s? I thought 100ma would offer enough discrimination from a 30ma? Read somewhere 3 times as much, so for discrimination 90ma or higher should act independently without the need for a time delay

An S type is used to ensure discrimination in all cases as far as possible.
Without a time delay fault currents could easily cause both devices to operate simultaneously. Also any background earth leakage on individual circuits could add together to bias the 100mA to trip first without the time delay.
 

Reply to My last 'non Amd 3' CU Install. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Looking for a bit of advice from the wider audience / those who may have done similar before. I entered the game a bit later / in a non...
Replies
12
Views
639
An interesting phone conversation with my own electricity supplier (Good Energy) which was very disappointing, and made me sigh (professionally)...
Replies
23
Views
9K
I do seem to pick only the weirdest properties to inspect... Victorian terraced house today - with up front RCD to a Wylex fuse board and main...
Replies
24
Views
3K
Doing one more of the flood of EICR today on a rented property before a tenant change, but ran into a slightly interesting case so would...
Replies
71
Views
13K
Hello, Would like some opinions. We have quite a few CU upgrades to complete. These are PRS properties, and looking down the list, a lot will be...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock