Discuss neutral fault ?? in the Australia area at ElectriciansForums.net

C

coxy84

been asked to look at a light in office unit that was diconnected buy another electricain 2 years ago, the lighting circuit is switch fed with the switch lines running though metal trunking (ceiling mounted) and in singles, the light is a end of line and had been disconnected at the light fitting before it.
between disconnected light and still connected light is an emergency light non maintained which has also been disconnected (neutral only).

the switch line for the lights are interconected loop in loop out and the the em light has a seperate line conductor.

they have a shared earth and neutral looped in and out.

with cables from working light fitting still diconnected i got a voltage of 230v between live and earth and neutral and earth at the non working fitting and at the em light.

but at the working fitting i get 230v live to neutral and live to earth and 0v between neutral and earth, there is no joins or damage to the cables between fittings.

i didnt get any shock off the metal fitting that has been disconnected so it cant really be live can it? but surely its to high to be a inductive voltage?

could it be something to do with the borrowed earths and neutrals?
 
Last edited by a moderator:
been asked to look at a light in office unit that was diconnected buy another electricain 2 years ago, the lighting circuit is switch fed with the switch lines running though metal trunking (ceiling mounted) and in singles, the light is a end of line and had been disconnected at the light fitting before it.
between disconnected light and still connected light is an emergency light non maintained which has also been disconnected (neutral only).

the switch line for the lights are interconected loop in loop out and the the em light has a seperate line conductor.

they have a shared earth and neutral looped in and out.

with cables from working light fitting still diconnected i got a voltage of 230v between live and earth and neutral and earth at the non working fitting and at the em light. Sounds like there is a feed from somewhere else. Is the neutral a switch live?

but at the working fitting i get 230v live to neutral and live to earth and 0v between neutral and earth, there is no joins or damage to the cables between fittings. Which is what you would expect

i didnt get any shock off the metal fitting that has been disconnected so it cant really be live can it? but surely its to high to be a inductive voltage?

could it be something to do with the borrowed earths and neutrals?


Difficult to visualise, but thoughts in red and at least it's bumped back up to the top:)
 
Has the disconnected neutral at the EM light also disconnected the neutral to the non working light? i say this because you say the neutral is looped in and out if the fittings.

I am also a bit concerned about you saying "I didnt get a shock of any of the metal fittings", and my worry is that you may have a missing live conductor in there somewhere which if it doesnt earth and take out the breaker, may well take out you.

I would isolate and have a very good nosey about for any missing cables, how many times have you come across someones cut off cables just stuffed into somewhere convenient to hide them cos they couldnt be bothered to do the job properly.

Cheers........Howard
 

Reply to neutral fault ?? in the Australia area at ElectriciansForums.net

Similar Threads

I hope someone can help with this as I'm stumped. My landing hallway ceiling (2016-build house) has two rose pendants which I've attempted to...
Replies
7
Views
417
Having a challenge understanding the concept behind why when you measure across line and neutral (live circuit) using voltage indicators we have...
Replies
25
Views
1K
Hi, have an old bathroom fan. Which has two wires the black and red (line and neutral). The fan has no isolator switch and was powered when the...
Replies
3
Views
648
Hi everyone, When checking my consumer unit voltages with the full board off, I stumbled across something head scratching. Measuring the feed...
Replies
1
Views
605
Hi, I’m new to the forum. Thanks for letting me join. Asking for some diy advicd… I’m trying to add a couple more security lights to the existing...
Replies
1
Views
614

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock